Surge Arresters on dual feed 5kV Switchgear

Surge Arresters on dual feed 5kV Switchgear

Surge Arresters on dual feed 5kV Switchgear

(OP)
I have a dual (primary and emergency) fed 5kV Switchgear that powers several pumps, fans, and transformers. The surge arresters are located on the load side of the primary and emergency breakers. These breakers can't be closed at the same time. The secondary side of the 2 transformers feeding this gear don't have surge arresters, the primarys do. It has been brought up that it would be best to move the surge arresters to the line side of the breakers to protect the secondary side of the offline transformer while that breaker is open. The switchgear and the secondary side of the online transformer would be protected with the closed breaker. Long question short, is it best to have surge arresters on the line or load side of switchgear main breaker(s)?

RE: Surge Arresters on dual feed 5kV Switchgear

it depends of distance between scary trasnfer ann load. make a sketch of xmtr, CB ,arester, load and distance

RE: Surge Arresters on dual feed 5kV Switchgear

it depends of distance between secondary transformer and load. Make a sketch of xmtr, CB ,arester, load and distance

RE: Surge Arresters on dual feed 5kV Switchgear

1-it depends of distance between secondary transformer and load. Make a sketch of xmtr, CB ,arrester, load and distance
2- Why to protect the secondary side of the offline transformer that is not in operation?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources