ESFR AND MULTIPLE ROW RACKS
Good day all
With regards to Table 16.2.3.1 of NFPA 13, if one has a ceiling height of 12.2m and a maximum storage height of 7.6m one can apply E.S.F.R sprinkler protection to class 1 to 4 products stored in multiple row racks.
Now under the definition of multiple row racks refer 3.9.3.7.3 of NFPA 13
3.9.3.7.3 Multiple-Row Racks. Racks greater than 12 ft (3.7 m) in depth or single- or double-row racks separated by aisles less than 3.5 ft (1.1 m) wide having an overall width greater than 12 ft (3.7 m).
If i use a K 240 (metric k-factor) head with a minimum starting pressure of 360kPa, am i correct in saying that no in rack sprinklers are required?
RE: ESFR AND MULTIPLE ROW RACKS
Many other variables shall apply to use ESFR, as ceiling slope that can not be exceeded, taking care of obstructions, etc.
Is there a limitation with regards to the maximum rack width?
I think, as long as you can satisfy the requirement of a single row, double row, multiple row rack arrangements, then you are good to go to follow the table 16.2.3.1
hope it helps,