what is the acceptable cretaria of IR Value for subsea HV cable( 40KV) and length is 40km.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
IR VALUE subsea 40kv cable
|
RE: IR VALUE subsea 40kv cable
Also, what is the age of the cable?
RE: IR VALUE subsea 40kv cable
RE: IR VALUE subsea 40kv cable
I would expect a new xlpe cable to give a tens of gigaohm reading for substation usage, so would expect something similar here (but I have not done any submarine cable work so am only guessing). If you vlf (very low frequency hipot) the cable with minimal leakage current it would prove the cables is fit for use.