IR VALUE subsea 40kv cable

IR VALUE subsea 40kv cable

IR VALUE subsea 40kv cable

(OP)
what is the acceptable cretaria of IR Value for subsea HV cable( 40KV) and length is 40km.

RE: IR VALUE subsea 40kv cable

What is the specification of the cable? xlpe? pilc? voltage? etc.
Also, what is the age of the cable?

RE: IR VALUE subsea 40kv cable

(OP)
XLPE CABLE AND 40KV RATED, NEW CABLE

RE: IR VALUE subsea 40kv cable

The supplier should be able to give some guidance (if the asset owner doesn't have any minimum acceptance criteria). Also supplier test results from factory testing may be helpful.

I would expect a new xlpe cable to give a tens of gigaohm reading for substation usage, so would expect something similar here (but I have not done any submarine cable work so am only guessing). If you vlf (very low frequency hipot) the cable with minimal leakage current it would prove the cables is fit for use.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources