NEC Table 430.250
NEC Table 430.250
Is there a formula for calculting amperes based on HP for the NEC Table 430.250? The table only goes to 500 HP and I have a 520 HP motor @ 575 VAC.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: NEC Table 430.250
For a particular motor, you should be able to get the full load amperes from the motor nameplate or motor supplier. Generally assuming 1 kVA per horsepower will be conservative. However, a 520 hp motor sounds somewhat non-standard, so you should try to get full load amp data from the manufacturer. Especially if it is submersible, hermetic, or unusually low rpm.
Bill
"Why not the best?"
Jimmy Carter