Staad pro plate modeling
My question is regarding the modeling of plate elements in a steel moment frame building using staad pro. I have all of my framing members put in and loaded accordingly. My flooring system is one way precast planks. My question is what would be the best way to model the precast panel to get the correct contribution of stiffness???
I did two small comparison models
1) with plate elements connected at each node of interesting beams
2) no plate elements
The two behaved considerably different, and my thought is that the model with the plate element is most accuate.
The second question does the size of these plates matter??? most of them are 10 foot by 10 foot if I only infill these in between my beam, or do they need to be smaller??
Any help is much appreciated, thank you
RE: Staad pro plate modeling
If it’s behaving differently than it must be from the diaphragm behavior. Before you consider that, you need to be sure it’s properly attached for diaphragm action. (I.e. some sort of mechanical anchorage to the supporting system that will transfer the forces.) Also, if it’s a one-way slab, likely a supporting girder will have to act as the diaphragm chord. If you don’t have the elements that will allow diaphragm behavior, it would probably be better to leave it out.
As far as what size plates to use: the typical acceptable limits to the aspect ratio is around 1:4 (the less the better; 1:1 of course being best). Of course (to tie in with what I say above) if they aren’t acting as a diaphragm it’s probably better just to represent them (self-weight and all) as loads.
I was thinking of having a steel plate cast into the panel with headed studs and then welded to the beam so i will get the diaphragm action.
The planks i beleive are cast as 15ft long and 4ft wide so i will be acting as a one way slab.
Thanks for your input.