Heat pump and electrical baseboard, continuous or non-continuous load?

Heat pump and electrical baseboard, continuous or non-continuous load?

Heat pump and electrical baseboard, continuous or non-continuous load?

(OP)
Hello,

I wanted to inquire if while sizing a main electrical service panel feeder or a sub-panel feeder, would the heat pump electrical load and/or any electrical baseboard space heating load be considered as continuous or non-continuous load?

Also while sizing branch circuit conductors, would the same classification apply?

Thank you.

RE: Heat pump and electrical baseboard, continuous or non-continuous load?

The answer I always give, is it depends. In Florda the heating is non-continuous. In Alaska it is continuous. However, any air conditioning would not be operating at the same time as the heating (we would hope), except in special cases (like our substation buildings). Anything that can operate for hours on end should be consitered continuous, but should be evaluated like the example I gave for conditions.

RE: Heat pump and electrical baseboard, continuous or non-continuous load?

Well, if you are sizing it now, I'd assume it was continuous. Per the NEC definition, continuous means three hours or more. I've always considered HVAC loads as continuous.

RE: Heat pump and electrical baseboard, continuous or non-continuous load?

Per the 2011 NEC (Sorry, I'm a bit out of date):

Quote:

ARTICLE 424— FIXED ELECTRIC SPACE-HEATING EQUIPMENT
424.3(B) Branch-Circuit Sizing. Fixed electric space-heating equipment and motors shall be considered continuous load.

So its a continuous load for the purpose of branch circuit sizing. And using engineering judgment, I'd say continuous for feeders and service equipment as well unless you can demonstrate diversity between multiple heating loads and excess capacity based on worst case heat loss sizing.

RE: Heat pump and electrical baseboard, continuous or non-continuous load?

Unless it has a thermostat. Most heating units are continuous.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources