Recommendation Needed for chiller to cool 6000 cfm air supply to -40 C

Recommendation Needed for chiller to cool 6000 cfm air supply to -40 C

Recommendation Needed for chiller to cool 6000 cfm air supply to -40 C

(OP)
Can anyone recommend the best way to chill a make up air supply of maximum 6000 cfm to as low as -40 C? Assume a max run time of the system to be 1-2 hours although the longer the better. If there are commercial systems available to do this please let me know what company(s) to contact.

Thanks,

Larry Jorgenson
PAMI
Humboldt, SK, Canada

RE: Recommendation Needed for chiller to cool 6000 cfm air supply to -40 C

And the entering temperature is?

It needs to run for 1 - 2 hours or longer how often?

The application?

RE: Recommendation Needed for chiller to cool 6000 cfm air supply to -40 C

(OP)
Application: Approx. 40' X 16' X 16' Environmental chamber with less than 20T cooling capacity at -40C. Able to cool the room to -40 C or colder for static testing of (non heat generating) objects and materials. Now we want to run vehicles in this room and still maintain -40C throughout the duration of the tests. Max cycle time would probably be twice per day but we would accept doing this only once per day and allowing it to take 6-12 hours to "recover". We are aware of the McKinley Climatic Laboratory and would like to accomplish something similar but only running conventional internal combustion engines say up to 60L in size. Typical machinery we want to test would be under 10L in size - we are estimating a maximum airflow to replenish the air used by combustion and remove the additional heat to be 6000 cfm.

Thanks.

Larry Jorgenson, P.Eng (Mechanical - U of S, 1994)
Prairie Agricultural Machinery Institute (PAMI)
Humboldt, SK Canada
www.pami.ca

RE: Recommendation Needed for chiller to cool 6000 cfm air supply to -40 C

In my experience, this type of cooling is usually done with liquid nitrogen or CO2. If your testing is not very frequent you don't even need a storage tank, just order a truckload for each test.

RE: Recommendation Needed for chiller to cool 6000 cfm air supply to -40 C

(OP)
Compositepro: can you expand on that? We have done some investigation into using Liquid Nitrogen but are there any references that you can point me to which describe the best practices for this type of use?

Larry Jorgenson, P.Eng (Mechanical - U of S, 1994)
Prairie Agricultural Machinery Institute (PAMI)
Humboldt, SK Canada
www.pami.ca

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources