34.5KV XLPE cables for Low Voltage Application
Contractor has a 34.5kV 1C x 300sqmm Cu/XLPE cable in their warehouse and suggested to used it in a 600V/1kV application. Is this possible?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: 34.5KV XLPE cables for Low Voltage Application
If the cable was to be used at a higher voltage where stress cones were required, then you would probably have to use the 34.5 terminating kits due to the physical size of the cable and approvals.
Still, check with the local inspector. His opinion is the only opinion that matters!
Bill
"Why not the best?"
Jimmy Carter
Just as a note, label, label, and more label whats going on as to eliminate a mix up.