Horizontal cracks in beam below slabs
http://img856.imageshack.us/img856/428/7cya.jpg
Has anyone encountered horizontal cracks in beam right below the slabs just like in the picture above? What could have caused it?
RE: Horizontal cracks in beam below slabs
Mike McCann
MMC Engineering
The designer who saw it told me it can't be from torsion because this only occurs in cantilevered slab. We don't want to chip if off yet and still discussing what it might be. Do you have any picture of how cracks from torsion looks like, or from the so called sliding failure where the T-beam flange has separated from the beam web?
this photo displays what happens because of rusting of steel. may be it looked like your beam on it's earlier stages .at this photo we can notice that the upper part of the damaged area is the most damaged part . which can tell that may be it begins with a crack at this part ..i can't see ur photo well but i think that there is another lower horizontal crack at the right side of the photo..
The beam is just one year old. It doesn't have the cracks a year ago. There is no post tensioning tendons. There are proper stirrups and bars. Perhaps in a T-beam, if the flange is very stiff and the beam twist, it can cause separation of the slab and beam?
Here is a hi-res photo not compressed:
http://img823.imageshack.us/img823/6323/n0oi.jpg
The stain above is just portion not painted well since the beam is just 10 months old.
In a T-Beam, won't it be possible the flange just separate from the beam web? You have slabs forming very rigid plane, then the beam underneath it. The thickness of the slab is 4 inches, the width of the beam is 12 inches. Would this be considered too large a ratio?
anyway i think there is nothing to be afraid of . because of the similarity of the structure insures that it was an immediate torsion and with small value. may be because of some deferent settlements . another reason to be free from worry that the spans arn't too large . and from the photo, the beem looks to have a good depth.
where r u from eng. Releky?
i think u have to check loads and design.
But I assume you have vertical shear reinforcement passing through the horizontal crack...hopefully with fully developed hooks that engage to the top long't beam reinforcing bars.
Yes, there are adequate vertical shear reinforcement spaced at 4 inches to 8 inches.. so the tension of each is enough to carry the concrete.. but the worry is the compression zone. The more loads there are and greater the compression, the horizontal cracks may be the weak part as it's above the neutral axis. How common is this case in practice, where the flange of beam has separated from the beam web?
Still looks like a restraint issue to me.
To add some value now, fill the cracks, see what happens over time. One more thing, now that this is no longer monolithic, composite behaviour of slab and beam requires horizontal shear resistance, check if the shear reinforcing is capable of this under design load, if not start busting up concrete.
We may eventually chip a bit to explore the extend of the crack, whether it cuts the entire slab/beam or on the surface like in the following (is this what you meant by restraint issue, what could cause the following)?
http://img824.imageshack.us/img824/4475/j0v7.jpg
Would this cause just a small crack near the interface as shown in the picture above or would this cause the entire separation of slab/flange from the beam?
http://img571.imageshack.us/img571/1747/fb1m.jpg
The reason there are many bars is because it is used for negative moments and it is L/3 in the beam span. For the rest of the span, there are just 2 compression bars to hold the stirrups. And oh, the stiirrups (0.4" (40 ksi) are distant 10 pcs at 4" and 8 pcs at 6".
Since the T-beam width (12") is 3 times the thickness of the slab (4") and the depth is 19.685", can the whole flange just separate from the beam web?
For perspective.
Dan97
Would this cause just a small crack near the junction as illustration earlier or would this cause the entire separation of slab/flange from the beam?
i assume that slab reinforcement is as shown in this pic ....i think it's sufficient to prevent separation
But in actual, the blue you draw is above the top longitudinal bars. The following is exactly how the slab bar frames into the beam.. it's spaced 1 foot apart...
http://img809.imageshack.us/img809/1623/2kxd.jpg
But I think the more bars, the more it can cause separation because you are introducing rigid plane into the slab/flange of the t-beam. Why, how do you think are slab bars should be arranged to prevent or promote separation?
No transverse top rebar over those beams?
We tried to chip off hoping it was just surface but the crack is deeper. If it is settlement cracks and since there are longitudinal bars just as the interface between T-beam flange and web (as shown below), won't this just be equal or literally cause breakage of flange from web (with only the stirrups holding the two together)?
http://img594.imageshack.us/img594/2712/s3f9.jpg
I agree with hokie66.
injection grout it if it will make you sleep better.
I just dont like this thin slab and heavy beam system and rebar ratio that can be seen on the photo. The amount of top rebar for the negative moment at the beam is unrelated to this crack, but i would be surprised if there's no crack in the length of the beam in the top of the slab.
that's the analysis of the beam .... there is no torsion at all on the beam even i put dead load and live load on just on side ( i expected some torsion when i do that but for my surprise there was no torsion. i don't really know why)
may be it's just a plastic settlement crack as the guys said
about the best arrangement of bars of the slab i prefer to put one bar below the longitudinal bars of the beam and the other above them.to resist any potential negative moment.
but there is a notice about no. of bars: for AS' the minimum number is 5 bars/m that means 1 bar @ 20 cm for assuring distribution of loads. u put 1 bar @ 30 cm i think it's quite little
http://img834.imageshack.us/img834/1993/wpsy.jpg
Hookie phased it: "The horizontal crack just below the slab is a plastic settlement crack. The plastic concrete in the beam settled, and the concrete at the top was held up by the bars. You may not have noticed the crack at first, but it was there."
And if this is common, how come you guys haven't seen one??
Also
http://www.concrete.net.au/publications/pdf/Settle... where the settlement cracks form up. With bars, please illustrate how the cracks can form in the beam just below the slab
http://img834.imageshack.us/img834/4268/u4ej.jpg
But in your case, there is a rigid group of bars to support the plastic concrete, and these bars also inhibit effective penetration of the vibrator, so the concrete below the bars settles under its own weight, causing the horizontal cracking below the beam bars, or probably in line with the bottom layer.
I have seen both types of cracks, both due to inadequate compaction.
http://img545.imageshack.us/img545/4990/6tyb.jpg
BA
Im sure they are exactly the same beam (the latter one with crack is one already painted white that's why the stains in the original picture gone). So I wonder if it's settlement cracks.. it could just be inside virtual the whole year then it slowly cracks outside because of concrete tension
BA
No, it's not visible. Just one side, so hopefully the flange-web is still at most half crack.
Can low viscosity epoxy get inside a crack as small as 1mm?
Yes, you can inject 1 mm (or smaller) cracks. You have to drill and install injection ports, etc. Suggest you consult with a specialist in this area.
"Can low viscosity epoxy get inside a crack as small as 1mm?"
Yes, assuming an experienced operator with correct pressure-injection equipment and resin, cracks less than 0.1mm can be successfully repaired.
Let's say the neutral axis is one half of the beam depth at service load. So the cracked flange and web is in the middle. One can think of a column with vertical crack in its half. With ties that hold it together, won't there be transverse pressure as axial strain increase (or compression strain in the case of a beam)? This means the ties or stirrups would be more stressed than usual if there is concrete crack as they have to resist the tranverse strain, or do you believe that even in uncrack concrete, the ties are working to resist transverse strain (or the beam stirrups resisting transverse compression strain in the compression zone of the beam)?
Here's the weird part. In over hundreds of buildings he inspected. He has never seen horizontal crack in beam one inch below slab. Most of you haven't seen it too except Hokie66. So how come only I and my crew and Hokie has seen such cracks. Is it so unique in the annals of structural engineering history that we should let the photograph appear in structural books?
Curious, what country do you practice? The very short span slabs with very thin slabs with 2-way beams reminds me of framing concepts prevalent in the Philippines back before 2000.
I have repaired a lot of cracks on concrete structures, including several horizontal beams cracks caused by cold joints, plastic settlement, restraint to shrinkage, incorrect PT drapes, etc etc. For a RC beams that is only 12" wide, low viscosity resin via pressure injection with an experienced operator will indeed fill the crack width and length, if deemed structurally necessary.
One project that had significant horizontal beam cracking caused by a cold joint, "leaked" cement grout during the PT grouting operations!
I practice in the Philippines. Why, have you visited it prior to 2000? Can you repair the horizontal cracks in the project?
Have you seen horizontal cracks near slabs or is it in middle of beam? The one who inspected it said he only see horizontal cracks in middle of beam, not near slab.
What Hokie66 mentioned about plastic settlement forming beneath bars made me realize one thing. Why you mustn't place beam and column concrete at same time, because after the column settles, a gap would form between it and the beam bars concrete. And the building can suffer moment magnification. In the Philippines, most contractors do column and beam pour together even in 50-storey buildings. Isn't it scary. In my neighborhood, an 8 storey buildings just falls to the ground (it's good the tipping is noticed at morning and all evacuation), then falls in the afternoon hitting another building. See video at:
http://www.youtube.com/watch?v=h5Z6itwKE0M
Maybe this practice of casting beam and column together must be outlawed? Almost all do it that way.
In case anyone wondering when the collapse occurred, here:
http://www.pinoy-pinay.be/news/20040723.htm
I think the bad effects of gaps in columns from beam-column placed together can only occur during strong earthquakes (as we don't have falling buildings often).
Does anyone know how to compute for settlement? Supposed the concrete has height of 400 mm and width of 300 mm.. what is the settlement distance in mm for a concrete of 4000 psi compressive strength, ready mix with admixture and fly ash. Does this settle more than normal cement mix? No one in my country knows how to compute for settlements so they don't separate column and beam placements but do them at same time.
As to plastic settlement, adequate compaction of the concrete and adherence to proper construction practices will eliminate these concerns. Prediction of crack thickness, when you can prevent the cracks from occurring, is poor thinking and not what engineers do.
The Canadian concrete code, A23 uses a factor k1 of 1.3 when calculating development length of horizontal reinforcement with more than 300 mm of fresh concrete below the bar. This recognizes the fact that bond in such bars is reduced because concrete settles, leaving a small gap on the underside of each bar.
BA
"Structural Engineering is the Art of moulding materials we do not wholly understand into shapes we cannot precisely analyse, so as to withstand forces we cannot really assess, in such a way that the community at large has no reason to suspect the extent of our ignorance." Dr. Dykes, 1976
The invited structural engineer suspects the formworks may also be a factor. In your country. How exactly do you do your formwork? The following is what is done in my country, leaks always occur at the interfaces. The second url below is the exact picture of the beams with formworks and leaking cement.
http://imageshack.us/a/img844/5611/jzcv.jpg
The following is actual picture of the leaking formwork. Standard in my country. How do you handle the leaks?
http://img835.imageshack.us/img835/8545/61l2.jpg
Steel bearers and bamboo joists for formwork. Been a while since I have seen its use. I was in Manila in 1999 and it was prevalent, and of course Hong Kong, but more so for scaffolding rather than formwork.
Those form "leaks" look about similar to what I have experienced in AU, US and CA.
I do note that is some parts of world, formwork chamfer strips for "external" edges are not as common as other areas. Correctly installed chamfer strips can assist in making the forms leak less.
For concrete members of depth of more than 300mm it is usual practice to re-vibrate concrete placement, to minimize cold joints, plastic settlement, etc. The concrete vibration task is often passed to the least qualified/experienced site laborer, and his/her duties are paramount to the success of otherwise of the hardened concretes properties.
So leaking formworks as shown in the illustration is normal? What country or place where the practice put putty around the formworks?
Ingenuinity, could you confirm if you have seen horizontal cracks in beams just below slab (one inch below) or is it more near the bottom or center of the beam?
Yes, we recently had a project where there was a horizontal crack about 50mm below the slab soffit on a PT beam that was 1000mm deep adjacent to a column - very congested top rebar and PT tendons and the concretor failed to adequately compact the plastic concrete. It was a localized crack to one beam of a total of 6. Was repaired via injection.
I do not believe the PT influenced the cracks in the situation Ingenuity has described. You have a large congestion of reinforcement, I would agree with several other posts here that it is lack of compaction and poor placement.
For your stated case, 1) your beam is deep (therefore more probable to be subject to plastic settlement), 2) is narrow (300mm), and 3) the top rebar is congested over the beam width - then 4) add in some inattentive concrete placement and it results in your horizontal crack. $hit happens. Point this out to future field construction supervisor or concretors and make them appreciate the consequences.
Can plastic settlement be avoided by compacting below it or is plastic settlement inevitable in spite of all efforts in the case of the beam I shown with horizontal cracks one inch below slab?
Or to rephrase it. If you will construct the same beam using exactly the arrangement of bars and beam width and depth (I shown). Is plastic settlement inevitable or can you do something that can totally avoid the plastic settlement underneath the 8 bars?
I'm a quality control engineer who checks finished construction.. so maybe I should take more part directly in the construction. Our ready mix concrete pumpcrete hose is 4" in diameter. We don't have smaller one. What smallest size have you use?
Below is the stirrup spacings of the 6 meter girder beam.
http://img844.imageshack.us/img844/5080/61q5.jpg
From face to face of columns, closed stirrups spacing starts at 1 stirrup at 50mm from column, then 10 stirrups at 100mm (4") spacing, 8 stirrups at 150mm
(6)" spacing and middle at 200mm (8") spacing. The beam is 500mm in depth, 300mm in width, there are 3 200mm (8") spacing stirrups at center (see picture) where 6-meter secondary beams on both sides framed into it. My concern is the contractor move one of the midpsan stirrup closer resulting it in forming 200mm, 100mm, 300mm spacings (see picture)..
Since the depth of the beam from tension bars to compression is 460mm.. half of it is 230mm... so one of the beam spacings at center didn't satisfy D/2 or 460/2=230mm because it has one 300mm spacing.
The following shows the shear and moment diagram at that location at 1.2 DL + 1.6 LL.
http://img38.imageshack.us/img38/457/gdp6.jpg
The concrete section + 300mm spacing stirrup has shear capacity V(c+s) more than the Vu (factored ultimate load).. which fulfills the spacing requirement but it doesn't satisfy D/2. According to the designer team and head, no problem with it since shear at midspan is not much. But I still have worry because it doesn't satisfy D/2. I told him what if diagonal cracks form there. He said he hasn't seen it happened. Now the reason I asked this is because I can have the 2 inches floor topping removed and change it to mere 3/4" topping to remove some Superimposed dead load to get even bigger margin.. the designer team and head said I can decide whether to do it or not. Isn't not satisfying D/2 in one of the stirrup a problem especially it is on midspan?
Designers in my country are not experts in physics. Most of them forget lessons back in the school days. My name is one of the signatories for liability. All codes require d/2 for the following reason (from http://site.iugaza.edu.ps/aalmadhoun/files/Chp5-Sh...):
http://img14.imageshack.us/img14/6434/479e.jpg
The reason for d/2 is to intercept any possible cracks. In the case of the one 300mm spacing of the 460 effect beam depth where d/2=460/2=230mm.. 300 exceeds 230mm. What if steeper cracks from 45 degrees form inside the 300mm spacing like in the following:
http://img809.imageshack.us/img809/8950/tk63.jpg
How do you think when working with this problem? Do you put close stirrups near midspan for concrete load to intersect steeper shear cracks than 45 degrees?
BA
i.e if Vu < 0.5*phi*Vc than shear reinforcement is not required.
EIT
www.HowToEngineer.com
In this photo, the bars look so close, I don't see how the aggregate could get between them.
http://img194.imageshack.us/img194/8761/e69l.jpg
Note the top layer is in the flange part and second layer is just below the flange like in the bar arrangement illustration shown earlier. There are one inch hole in between the bars as required by code so the aggregates should flow in between them.
RFReund, Vu is > Vc, that is why stirrups are required.
hokie66, Is it not that steep cracks are combination of flexural cracks and diagonal tension cracks called flexural-shear cracks. Near midspan, I can imagine the flexural cracks forming vertically then it gets at an angle signifying start of diagonal tension cracks. Have you ever used Respond-2000? It can model how the crack exactly form and even width but I'm preflexed why in the following with the sections and bars data inputted, it only shows up to 119 KN. Who has tried Respond-2000 before? (freeware at http://www.ecf.utoronto.ca/~bentz/home.shtml)
http://img543.imageshack.us/img543/3206/ee7f.jpg