FM Approval 3611 - Instricially safe
If you look at the ignition curve for resistive load, Figure B-1 page 28, I'm surprised by what the FM shows vs. some of the post that are listed on this site for intrinsically safe. Most intrinsically safe that I have worked with keeps the power minimal, in the mW, however, from the graph, 12V @ 5A will not have enough power to spark/ignite the gas? If this was the case, then 60V should be able to go to 1A, however, this is not the case according to the graph. The only thing I can thing of is maybe 12V is not enough to cause a arc between the air gap, ie switch closing and the voltage gradient increase as the switch gets closer to the contact point? Has anyone actually proved or done a test of this nature with explosive gas and arcing 12V with 5A?
guilio
guilio
RE: FM Approval 3611 - Instricially safe
Best to you,
Goober Dave
Haven't see the forum policies? Do so now: Forum Policies
I believe you are correct that the 12V won't spark; I have an old reference showing about 34KV/in at room temperature and sea level, so 12V won't jump a gap larger than 0.3 mils.
Z