What is the recommended minimum cover over Class V RCP? Where can it be found? Any help much appreciated.
What is the recommended minimum cover over Class V RCP? Where can it be found? Any help much appreciated.






RE: Minimum cover for Class V RCP
http://www.concrete-pipe.org/pdf/FillHeightTables....
Note that Class V pipe that you are asking about is suitable for highway loading with only 1 foot of cover (the minimum shown in the tables) even if there is no bedding at all (Type 4 Installation). One foot is generally considered minimum cover for practical purposes. You did not state the loading for your application, but if it is higher than highway loading, you may need either more cover or a "Special Design" pipe.