Bursting of concrete after stressing
Hi all
In one of my project, the concrete always bursts at the stressing ends of 200 mm thick slab tendon anchorages after stressing.
So I checked the things below
(1) Stressing jack - It was calibrated and used that jack for other projects and nothing happened.
(2) Bursting links - I used (bursting force = 0.23 Pre-stressed force)and provided more than enough links.
(3) Anchorages size - Our anchorages sizes big enough to transfer the force to concrete.
(4) Insufficient concrete strength - that is the plausible cause I can think of. The concrete grade is 35. Do we need to use an admixture for grade 35 concrete to control the heat released from cement. If it was due to concrete, I need some evidences to substantiate.
Can you think of any other causes?
RE: Bursting of concrete after stressing
Kieran
2. What was the strength of the concrete slab at time of stressing?
3. Did you use Lok tests to determine the in-situ concrete strength before stressing? I always specify Lok tests for prestressed concrete; field cured cylinders placed on top of the slab are no good for this purpose (or for any other purpose).
4. Have you taken any cores to check the concrete strength?
5. Has the weather been cold and slowed the strength gain?
6. Do the links have proper development length?
7. Did anyone inspect the placement of the links before the concrete was placed?
A piece of advice: Don't do any more prestressing until you have determined the cause and addressed it. Bursting cracks can grow with time. About 30 years ago we were called in to investigate a beam that collapsed due to this issue. It collpapsed 9 months after the garage had been opened for use. In that case, there were no links provided, so that would have been worse than your case.
Sometimes the only way to get rid of cracking is to reduce the p.t. force. I find that it is much better to use less p.t. force than more i.e. use partial prestressing. What percentage of the dead load did you balance?
Also, you might try using the strut and tie model to determine the bursting force.
I think your problem is due to some combinaion of the factors that I listed in this post and my immediate previouse one.
Be sure that you find the right in-situ strength before stressing the tendons. Use either Lok tests or maturity meter method. I prefer the Lok tests.
Dik
1) It is normal weight concrete.
2) At time of stressing, the concrete strength is so strange. Within three days, it was around 55 Mpa.
3) Didnt carry out LOK test. Just cube test.
4) no
5) If it was raining, does it affect the concrete strength.
6) What do you mean by development length?
7) Yes, my site engineer inspected before concreting.
Used As required = bursting force/200 which is according to CP65.
Precompression is around 3Mpa.
dik,
It was 5 strands flat slab anchorage.
Agree with ajk1....do insitu strength testing as that is more accurate for the stressing conditions than the lab condition...
ajk1....seeing your reference to LokTest brought back memories of John Bickley introducing me to that in the early 80's. It's not used down here, but got experience with it in my association with Trow. Good method.
Struggle66 - I have a conference call in 10 minutes, but after that I will try to get back to you. The development length Ld is given in the various codes/stanards by formula (example: CSA Standard; ACI 318, etc.). If you don't have adequate Ld from the point of maximum stress of the link, to the end, the link may have some loss of bond to the concrete and open a crack. How thick is the slab that you are post-tensioning and what size (diameter)are the links? Did you design it, or someone else?
2. Is there a 25% initial stress prior to full stressing?
3. Any visually-observed boney/honeycomb concrete at anchorage zone/s?
4. Is the anchorage rebar a standard rectangular spiral, or 2 pairs of ties?
According to CP 65 Ld is from 0.2Yo to 2Yo behind anchorages.
where Yo = half the side of loaded area.
I assumed the loaded area 200(slab thickness) x 350 ( minimum spacing between two flat anchorages).
So I used Yo = 200 as bursting is critical in Y direction.
How do you calculate Ld?
The concrete concrete was bursted so badly. Sometime without bursting the anchorages drew into the slab seem like concrete bearing failure.
One more thing our anchorages broke once the concrete failed. Is raining will be a reason?
One anchorage only bursted only after a few days. I am scared that it will happen again after the building has been opened like you experienced.
Dik
It is hard to say for sure without seeing the drawings and details, and perhaps I am misunderstanding the situation, but I fear that you have a design problem, not a concrete problem. If your slab is only 200 mm thick, then the links cannot be fully developed. I believe that the Code notes that stirrups cannot be developed in slabs less than 250 mm thick. Also, you should check the Code as to what stress you should design the links for. The PTI manual used to say to design for 30,000 psi, not for the 60,000 yield strength of the bar. Not sure what it says now, as I am not in the office. Studrails are usually used in slabs of this thickness. Another solution is have fewer tendons per anchorage and spread the anchorages farther apart.
Can you attach a sketch plan and section of the anchorage? It sounds like there is a very serious problem...sorry to be the bearer of bad news...this is one time that I hope that I am wrong. I think your best coaurse is to retain an engineer who has sepciualized in prestressed concrete design, to review your design.
Where are you located and to what Code are you designing?
There are two types of reinforcement around the casting which I am familiar with: 1) two bars top and bottom continuous along the edge, with ties around these bars, and two ties on each side quite close, and 2) a rectangular spiral around the casting. Which do you have?
ajk1, I don't know how the slab shear, studrails etc., comes into this. He is talking about bursting of the anchorage.
The concrete strength result sounds very strange indeed. 20 to 25 MPa is normally sufficient.
Links yield stress is 460 MPa but I only used 200 MPa according to CP 65. In Singapore, they adopted BS as CP 65.
My company is PT specialist company in Singapore. We have been using the bursting links as per our company standards. Nothing was happened for many other projects.
Later I will attach sketch and detail for you. But now FYI,
It is an one way pt slab with seven (8.6 m) spans and with PT beams spanning in transverse direction. The concrete bursting locations are at the pour strip located at the one-third of the fourth span.The tendon spacing is around 1.2 m. Anchorage size is 90 x 300. 5 T 13 rectangular(300 x 120) closed links with 70 mm c/c were provided just behind the anchorages.
Thanks for your advice. Now we are using 5 strands tendon per anchorage but later I will design with 3 or 4 strands per anchorage for thin slab(<200) and will highlight my company to carry out LOK test before stressing.
Our anchorage supplier is OVM from China.
Yes anchorage are centrally located at slab (C.G is 100).
It is 0.6 in dia strand stressed till 75 percent of breaking load.
First we stress 25 percent and then 100 percent.
We use rectangular closed links as mentioned above.
It appears you are using a variation of the attached DETAIL 2, prevalent in South East Asia, whilst the rectangular spiral (DETAIL 1) is more common in Australia. These details have been used in thousands of bonded PT slab systems without incident, other than the occasional failure primarily due to unconsolidated or low-strength concrete.
Without seeing a photograph of the failed PT anchorage zone/s, my guess is that the pour strip where the PT anchorage zone/s is/are failing is due to: 1) unconsolidated/vibrated concrete - is there evidence of boney/honeycombs at the anchorages? 2) the concrete batch placed at the subject pour strip was incorrectly supplied or understrength.
Is it possible to take 3 each 100 dia x 200mm deep field cores at the pour strip area and undertake compressive strength testing to determine probable cause?
To fix failed PT anchorage zones are a real pain, especially when there are multiple failures. The general contractor gets upset too - forms have to remain in place longer, and the construction schedule gets problematic.
If you have a photograph of the failed anchorage zone please upload it and share it with us.
The way I interpreted his detail is that he is using a modification of Detail 1, with individual closed ties used rather than a spiral. If that is the case, I would be concerned about development of the ties. If the concrete or the anchorage reinforcement is suspect, 5-15.2 strands is a lot of force.
Yes you are correct about the links detail.
Here with attached failure zone photos. In the last photo the anchorage just drew into the slab.
I would not be blaming the rain.
Sounds and looks like low concrete strength to me and possibly bad compaction.
We would need to see how the ties are position at the anchorage to see if they are effective. The area supplied should easily be sufficient. Normal requirement would be 4 R10 ties, so about 1/2 of the area supplied and I think development would be ok as long as they are closed ties as you are only trying to develop about half of the strength of the bars anyway. But the positioning and the compaction are critical.
Uploading agian. My bursting links are not spiral so I think they cant resist the force together in a combined action. Is it still ok?
Kindly see links detail.
Is it actually placed like that relative to the anchorage?
How can they achieve proper compaction around the anchorage. The ties are very close together. Are you end up with slurry run into the anchorage zone will very little aggregate and /or bad compaction?
Looking at the failed anchorage, the failure appears to be in the fines, not through the aggregate which would mean low concrete binder strength at the timer of stressing. Where were the cubes stored before testing for the timing of the stressing operations?
We also upped the amount of bursting steel.
Also, it might be better to get site cured samples to better match the strength gain versus cubes that are in a controlled environment.
And importantly, like others have said, there should be adequate compaction around the anchors.
Oil on the strands will affect bond, but this only plays into a dead-end anchorage zone during stressing, not a live-end like this instance.
Also, whilst a 3 strand tendon will much reduce the bursting and anchorage stresses, it will increase the PT cost substantially - PT supply and install is all about trying to maximize the number of stands per 5-strand anchorage, and maximize spacing and tendon length.
5 strand tendons have been used successfully without problems for 30 years in countries where there is good control of concrete quality in all areas from mix design to compaction to strength determination and with well made anchorages using good quality cast iron (SG instead of Grey).
If you cannot get all of these right, you should not be doing prestressing at all.
However, for multi-strand bearing/anchor wedge plates, they are often CNC machined, so too are multi-strand coupling blocks.
I have to raise this thread again. In BS 8110, CP 65, at end block of stressing anchorage it does not mention to check the bearing capacity of concrete. But when I looked into ACI, the following simple equation needs to be satisfied.
0.6 x 0.85 x fc' x Root (A2/A1) > 1.15 Pj / A1
The capacity can be increased by 50 % if the concrete at end block is confined inside bursting links with a maximum recommended value 0.6 x 2.5 x fc'.
When I check concrete bearing capacity for this project, it was failed.
I believe that is what happened in my project.
Thanks all for your answer before.
The actual bearing stress depends on the anchorage shape. If it is a typical slab type anchorage, the standard bearing rules do not apply because they are not a flat bearing plate. In cast anchorages Force is transferred over the length of the anchorage (sloping sides) and also by fins along the length, so all of the force is not being applied at the front face of the anchorage and thus the actual bearing stresses are smaller. Normally these anchorages are proven by testing as is allowed by the anchorage codes.
I would still be betting on low grade grey cast iron being used in the anchorages instead of SG Iron!
Perhaps you have an oddball anchorage that is smaller than normal and has not been load tested, but much more likely causes are:
a) that the rebar links are not being fully developed, as there is insufficient development length available if the slab is only 8" thick (8"-1" cover top and bottom = 6". leaving only 3" development length available from the plane of maximum bursting stress!!; I would never rely upon rebar links to take bursting force in a member only 8" thick) a
and/or b) you have the anchors too close to each other. What is the spacing between anchors?
Have you tried turning the anchors so that their long dimension is horozontal rather than vertical?
My experience is that splitting cracks in the anchorage zone can worsen with time and are a very very serious issue.
I strongly recommend that you retain an engineer with specialist experinece in post-tensioned concrete to advise you. A few hours of his/her time will be more than worth it.
There is only one fin in our anchorage and the slope is almost horizontal. Is it appropriate if I distribute the bearing stress depending on the area of the face behind anchorage and fin? And then I will check the bearing. I have also requested anchorage supplier for any proven test or example calculation.
ajk1,
(a) For the rebar links I utilized only 200 Mpa for 460 Mpa steel.
(b) Spacing around 700 mm. Longer dimension is horizontal.
Test them yourself. The Australian code covering testing should be AS1314. I am sure Europe has an equivalent and presumably ACI does as well.
I received test report from supplier. They carried out the test on 225mm thick concrete block sample with concrete strength 50 MPa. Now my slab is 200 mm and concrete strength at time of stressing is only 25 MPa.
Working without a mentor is not easy for me. Everything I have to do it on my own and your answers are always helpful for me.
It was intentional.
I was surprised when I saw this test report. I dont know about other parts of the world. But in here the practice is to stress at 25 MPa.
You need to get a copy of the Anchorage design/test code relevant to your country and check that the tests are in accordance with nit. I assume the 25MPa is cube strength, is the 50MPa cube strength also?
It also depends on the concrete mix. You need to test the anchorages yourself under the conditions you use them, e.g. concrete mix etc.
The whole problem here is really in your last sentence. A PT company is supposed to be providing a high =technology sub-contracting service. It is supposed to make sure that the materials it uses are up to spec. Unfortunately the PT industry (I am now talking bonded outside USA as USA has its own problems) has developed to a stage where anybody thinks they can run PT comp[any. This has led much lower prices but also much lower standard of technology within the PT companies.
(start rant)When I started in PT many years ago (and the same for ingenuity, we designed and tested our own anchorages, wedges, blocks and even the duct and bar chairs. I might have started as a graduate engineer but I had several experienced engineers over me as well as a worldwide technology base within the company. But this costs money and requires much higher PT rates. These days, everything is purchased off the shelf, the senior engineer (if there is one) is a recent graduate and there is no technical knowledge within the company. And we end up with situations like yours where you are relying on questions to a free online forum to provide your companies technology backup. In the interests of the industry and engineering in general we should not be answering these questions!! (end rant)!
50 Mpa is cube strength.
I am not trying to improve my company technologies and standards.Even if I suggest something(for example not to use average moment method)to my company, they will not accept it because it does not lead to lower prices. I just want to know what I am doing. I just at least want to work like an ENGINEER! unlike a business man who only care about money. You wont believe if I say there are so many designers in here who don't care or don't know about structure even in structural consultants firms.I will not give up trying to become a TRUE engineer. Hope my dream come true although it is not easy for a recent graduate with lower education background. :D
thanks all
We do believe you. Sad, but true, and not just in your country.
I am not criticizing you, it is companies like yours and the "business men" who run them. What you have said about your company and others is exactly what I meant. You have been forced to be in the position that you are in and to rely on help from sites like this because of their attitude.
It is a sad direction for both construction and the engineering profession as well as the world in general!