Switchgear Redundant DC Battery System

Switchgear Redundant DC Battery System

Switchgear Redundant DC Battery System

(OP)
I have a customer wanting a fully redundant battery system, their design is each battery feeds and ATS which then feeds a DC distribution panel out to the switchgear loads. I'm looking for thoughts or white papers on their design vs. paralleling two batteries directly to the DC panel & having each charger connect to a branch circuit in the DC panel.

RE: Switchgear Redundant DC Battery System

What's the matter, you forgot to include the cost of the ATS your bid?

Why do we get this constant stream of "my customer wants ______, but I want to do ______ instead, how do I talk them into it" questions?

If the customer wants something, why not just provide it? They're the one's paying the bills. If you left something on the table at bid time just suck it up and be a big boy. A contractor's favorite way of doing things is just the contractor's favorite, but it is the owner who gets to make the decisions and they get to have it their favorite way.

RE: Switchgear Redundant DC Battery System

(OP)
We are currently working on bids and have no issue providing the ATS, I'm just trying to educate myself so if a customer asks my recommendation I have an opinion. Also, the customer put the responsibility of designing the DC system on the switchgear manufacturer.

RE: Switchgear Redundant DC Battery System

The disadvantage to in the alternate approach you propose is increasing the probability of a common-mode failure taking down the entire system. Also, you probably don't want the batteries and chargers all tied to a common bus - one failed or dead battery will take all of the charging current from both chargers, as well as drain the good battery. The batteries need to be isolated from each other.

RE: Switchgear Redundant DC Battery System

Two batteries, two chargers, two Dc panels. One feeds trip one, the other feeds trip two. That is what I would have specified, and then I would have had to had to hear how excessive that is.

The ATS seems to be a common mode problem. However this is distribution so maybe it dosen't matter to them.

RE: Switchgear Redundant DC Battery System

I agree that the original design also has some common mode failure issues. Two completely separate systems would be more reliable. The most common thing I see fail on dc systems is the battery charger.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources