2012 IRC braced wall lines
2012 IRC braced wall lines
(OP)
thread507-319099: 2006 IRC 602.10.1 Braced Wall Line Offsets
The 4' offset is shown on one level. I don't see anywhere indicating that it has to stack over the one below. In fact, figure R602.10.8(2) suggests that the wall panels do not have to stack. The only mention of them having to stack that I can find is Section R602.10.2.1 which references R602.3.5 stating that the braced wall panels must stack if they provide a wind uplift path for the roof framing.
Does that mean that braced wall lines (say interior walls) don't have to have to align or even be within 4' floor-to-floor?
The 4' offset is shown on one level. I don't see anywhere indicating that it has to stack over the one below. In fact, figure R602.10.8(2) suggests that the wall panels do not have to stack. The only mention of them having to stack that I can find is Section R602.10.2.1 which references R602.3.5 stating that the braced wall panels must stack if they provide a wind uplift path for the roof framing.
Does that mean that braced wall lines (say interior walls) don't have to have to align or even be within 4' floor-to-floor?






RE: 2012 IRC braced wall lines
RE: 2012 IRC braced wall lines
Typically i would not utilize a non-stacked interior wall, it makes for an ugly load path and cause complications during design, and often has serviceability issues. However, i have made first floor interior walls with no second floor wall above them.
RE: 2012 IRC braced wall lines
RE: 2012 IRC braced wall lines
R602.10.1.4 Braced wall panel location (...) All braced wall panels within a braced wall line shall be permitted to be offset from the designated braced wall line.
also of interest
R602.10.6 Braced wall panel connections.
R602.10.7 Braced wall panel support.