Transformer inrush current
3

Transformer inrush current

Transformer inrush current

(OP)
Dear Friends,

Could anyone please clarify that the transformer inrush current (6 to 12/14 times) normally specified based on Transformer ONAN rating or ONAF rating?

RE: Transformer inrush current

The inrush current is based on the ONAN rating normally.

Regards

RE: Transformer inrush current

(OP)
Thank you Bigamp and jbartos

RE: Transformer inrush current

From oscillography records during energization of a 15 MVA 100kV-12.47kV transformer (unloaded):

Peak inrush (around 2 cycles) Phase A 1.16 x full load amps, Phase B 2.76 x full load amps, Phase C 2.56 x full load amps.

Phase A inrush dropped to 1.13 x full load in 25 cycles.

Peak differential relay operating current was 1.77 x full load.  Peak second harmonic current was 1.07 x full load.

RE: Transformer inrush current

(OP)
Dear All,

The rating of the transformer, I am referring is 15/22.5 MVA, 13.8/34.5 kV, ONAN/ONAF, Z = 10 % step up transformer.
In absense of the manufacturer's data for magnetising inrush current, I have the following doubt:

The magnetising inrush current should be considered as K times the current rating on ONAN rating i.e (K times 627 Amps) or K times the current rating on ONAF rating i.e (K times 941 Amps)?

Please advise.

RE: Transformer inrush current

I agree with bigamp that the typical values normally used are based on the ONAN rating.  Keep in mind that there is no standard for what the inrush will be, and it is not something that is normally "specified".  Values typically assumed for distribution transformer protection (from Cooper Power Systems Fusing Manual) are:

2 times full load @ 100 sec
3 times full load @ 10 sec
6 times full load @ 1 sec
12 times full load @ 0.1 sec
25 times full load @ 0.01 sec

RE: Transformer inrush current

Correction to my previous post on energizing a 15 MVA 100-12.47 kV transformer:

Inrush at 25 cycles:  Phase A 0.55 x full load, Phase B 1.25 x full load, Phase C 1.13 x full load.

RE: Transformer inrush current

It also depends on exactly which point on the wave you happen to be at when you switch on.  It is alos affected (particularly duration) by the amount of load on the transformer.  I think the rule of thumb values normally quoted are extreme worst case - it is pretty difficult to choose a reasonable fuse rating based on the ransformer size when it has also got to be able to handle 6x for 1 sec, 3x for 10 sec when it is standing outside in the full sun on a 40C day!

Bung
Life is non-linear...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources