hi every body
I have two lines Feed my project at 8 bar , the first line feed for the landing valve
and other feed zone's and fire hose reel.
in hydraulic calculation of zone sprinkler neglected 7 bar of landing valve ??? or what can i do
pleas advice

RE: question in hydraulic calculation

as per NFPA 13, the calculation must be performed for each system (Standpipe, sprinkler and etc) and not in combination of two systems. In case you are calculating sprinkler system in hydraulic calculation, you don't need to consider the standpipe connection as a standpipe demand but only a hose allowance.

RE: question in hydraulic calculation

(OP)
GeorgeMech,

Thankful for your response

RE: question in hydraulic calculation

George,

That's not always the case. For a building with a LH or OH-1 or OH-2 discharge density combined with a Class I standpipe, the standpipe can be more hydraulically demanding. I currently have a sprinklered 27 high rise on my desk with 3 standpipes. The 1,000 GPM @ 100 PSIG at the highest floor is far more demanding than any on the OH-1 or LH discharge densities.

RE: question in hydraulic calculation

Stookeyfpe,

Yes it is true and most of the cases standpipe system is more demanding compared with sprinkler system, my statement is only to clarify the question of zicooo regarding on combining the standpipe system and sprinkler system in calculation, although, NFPA also states that if the building is partially sprinklered, you must combined the two system in order to get the system demand.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources