The architect wished to discontinue the floor sheathing at party walls between adjacent units. (this will leave 1" gap that will be filled with fire stop metal strip). By doing this, floor diaphgram discontinues. Shall I design the party wall on each side of the gap as a shear wall?? or shall I consider the fire stop metal strip as a continuation of the floor diaphgram??
Please advise
Please advise






RE: Sesimic design of wood frame multi-family yownhomes
Mike McCann
MMC Engineering
RE: Sesimic design of wood frame multi-family yownhomes
Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
RE: Sesimic design of wood frame multi-family yownhomes
When we see this detail from architects, we ask them to revise to show the sheathing continuous. Sometimes they will revise to show fire-resistant sheathing for a certain distance each way.
RE: Sesimic design of wood frame multi-family yownhomes
Are yownhomes part of a new HUD program in Texas?