A/C Induction Motor Run-in
A/C Induction Motor Run-in
(OP)
I understand that it is necessary to perform a run-in on brushed D/C motors because the brushes have direct contact with the shafts and this could affect alignment. Is it necessary to perform run-ins on A/C induction motors? The stator and windings don't actually touch the shaft. The only thing it might affect is how the bearings are seated... But could this really change that much (enough to affect the alignment)? I am discussing this in the context of industrial plants where the pump drivers are almost always A/C induction motors. In essence, how important is it to perform a run-in on an induction motor prior to final alignment?
Thanks for any help!
Thanks for any help!





RE: A/C Induction Motor Run-in
I have never known a run in on a pump motor set, what you need is to get hold of the suppliers installation manual, then if there is a requirement to run in it will be detailed in there.
RE: A/C Induction Motor Run-in
RE: A/C Induction Motor Run-in
Have a read of this alignment installation
http://www.plantservices.com/assets/knowledge_cent...
RE: A/C Induction Motor Run-in
RE: A/C Induction Motor Run-in
"Motor run-ins shall be performed prior to the start of final alignment activities. If final alignment precedes the motor run in, the alignment shall be rechecked after the motor run-in has been completed."
The comment made no sense to me because the manufacturer would already have run the motor during Factory Acceptance Tests...
I was just wondering what they could possibly mean by this. After doing some reading it seems that a motor run-in is only really done on a brushed D/C motor that has never been run before...
RE: A/C Induction Motor Run-in
Then again, it's been a long time since I've looked at any new DC motor installation...
"Will work for (the memory of) salami"
RE: A/C Induction Motor Run-in
Can you explain what you mean by that?
I've heard of run-in of dc motors to help the brushes to conform to the radius-of-curvature of the commutator (see another current thread on dc motors). But I don't see how it relates to alignment.
=====================================
(2B)+(2B)' ?
RE: A/C Induction Motor Run-in
=====================================
(2B)+(2B)' ?
RE: A/C Induction Motor Run-in
Then just run it.
Checking (and recording) the bearing temperatures occasionally during the first days of service is probably a good idea, more so for very expensive motors. ... but then for very expensive motors you'd have bearing temperature monitors installed and connected to alarms or shutdowns, wouldn't you?
Mike Halloran
Pembroke Pines, FL, USA
RE: A/C Induction Motor Run-in
I visited a plant with large screw compressors some time ago. EDM problems. The motor manufacturer had put a shaft grounding brush on NDE and placed it close to the bearing. So close that the grease migrated along the shaft and eventually isolated the brush from the steel surface.
There, the same discussion regarding run-in of the motor was going on and the shop was divided into two "parties" - the run-in-sympathizers and the anti-run-inners. They were ridiculing each other and nothing had been done to remedy the problem. They created a mind-block from a misconception and while they were discussing that non-issue, the bearing failed.
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: A/C Induction Motor Run-in
"5.4.1.2.3 Axial alignment shall be done after the motor magnetic center is marked during field or factory run-in. The motor shaft shall be located on magnetic center. If the motor cannot be run for magnetic center due to an end fan, the motor manufacturer must specify the shaft position."
Which is implying that mag center is found by doing a "run-in"... Maybe the ppl who wrote that paragraph had a little screw up?
RE: A/C Induction Motor Run-in
Sounds like the customer just wants to see some hours on it without anything bad happening. It sounds like you are to align the motor and load, run it for a certain length of time (is the time specified?) and then align it again.
RE: A/C Induction Motor Run-in
In most AC motors you will have a bearing that is locked in an endbell (PE or OPE) and the opposite may have a spring washer to take up the endplay slop. If you are not using a rigid coupling you have to be sure to check and make sure there is enough clearance between the coupling halves. You do not want the halves to touch or you will run into issues with vibration and could possibly lead to axial pressure bearing damage.
If you need any further information visit the Repair Zone Learning Center, or contact Repair Zone customer service for Technical support.