Understanding Shear Friction
Good afternoon, all:
I had a question regarding the way ACI-318 handles shear friction. My understanding of the concept is that at, say, a retaining wall's base which was poured separately from its footer/slab, shear resistance is provided by the compressive component of the moment couple caused by flexure in the wall. What I don't seem to fully grasp is that in ACI-318, the equation for shear friction resistance is Vn=Avf*fy*mu ..... that is, it doesn't use the actual or factored moment-couple force, it essentially uses the flexural As*fy. This might make sense to me if the wall has just enough steel in it to resist its Mu, but what if you've got additional flexural steel in the wall? Am I to understand, based on this equation, that shear resistance due to friction can be had by adding flexural reinforcement that will never approach its fy under factored loads? And that this shear resistance is available no matter what the flexural loads in the wall are? (i.e., if you apply a horizontal point load very near the wall's base, say.) I suspect that there's a nuance to this that I'm not appreciating, so any light that you fine people can shed on this would be much appreciated.
RE: Understanding Shear Friction
So to answer your question, adding steel above what is required for moment resistance will in fact increase the shear resistance. As the additional reinforcement yields there will be an increased clamping force across the shear plane (Although the commentary does suggest that additional shear friction reinforcement beyond that required for flexure be placed primarily in the flexural tension zone)
But the situation you are describing is much like a corbel bracket (high shear and small moment) in which case the required area of shear friction reinforcement may be much larger than required flexural steel.
Back to your example. If all of the flexural steel is yielded then the clamping force (compressive component of moment couple) equals the tension force in the reinf = As* Fy. If additional steel is added, the clamping force due to flexure would = As* Fs. As the wall and footing try to move relative to one another due to the application of the low horizontal force, additional tension would develop in the reinforcement creating a greater clamping force.
Shear breakout may still be a valid concern with small edge distances. And you should also be careful that you do not end up with an over-reinforced section for flexure.
As I understood it, and I never use it, mind you, either, it was the theory that in order for the vertically irregular concrete surfaces to slide one against the other horizontally, a very small amount of vertical displacement, or lift, would have to occur between the two concrete elements to reduce the friction to allow the sliding to occur (assuming the concrete surface would not shear off these elements), and this lift was to be restrained by the vertical shear-friction steel, thus maintaining the frictional resistance.
Approved or not, I never rely on it solely on it's own merit. Maybe ass an undocumented safety factor, but that's all.
Mike McCann
MMC Engineering
http://www.eng-tips.com/viewthread.cfm?qid=122089
Msquared, if you do not rely on shear friction, how do you account for the shear across the shear plane between two non-monolithic surfaces (such as a retaining wall and a footing as described above). Shear keys? Breakout prisms @ dowels per appendix D??
Although many of us no not make use of the shear friction equation everyday, shear friction is still used on a regular basis as the primary mechanism to resist in plane shear across surfaces.
The increase in friction allowed is only due to the presence of the interstitial reinforcing steel.
Mike McCann
MMC Engineering
My understanding is in line with Mike's. What seems to not make sense is how it works for steel against concrete. For concrete on concrete, aggregate can cause movement normal to the shear plane to engage the bars in tension and apply the normal force, but for something smooth, like steel, against concrete, I don't see that same mechanism as being realistic.
Mike, when you design the bars for shear through the bars at the base of a wall, how do you account for breakout if you have only 1.5" of edge distance? I've never seen in ACI that using the bars in shear is an acceptable method of transferring shear across a plane - did I miss that?
I generally do not rely on the steel, but either bearing against a slab, or a shear key in the wall. I just feel better about it.
Mike McCann
MMC Engineering
I'll stop right there though... Enough said.
Mike McCann
MMC Engineering