Where's the energy going?? Heating Air with Steam
Hey Folks,
I'm interested in an open discussion for a phenomenon I'm seeing. Basically I am heating an incoming air stream on a drier with steam, I calculated the Q requirement to heat my air stream be on the order of 5MM BTU/hr, however the flow controller and steam pressure says im using 10MM BTU/hr of steam to get there.
I'm confused, where is the other 5MM BTU/hr of steam going??? I'm just guessing that a lot of the steam is not condensing and its got to be going out with the condensate before giving up its energy...I imagine if I had a 5MM BTU/hr leak this is something that would be pretty apparent. What is a typical range of efficiency of a fin/tube heat exchanger with air on the fins and steam on the tubes? Wheres it going?
RE: Where's the energy going?? Heating Air with Steam
At 100% efficiency (i.e., zero heat leakage), you are actually adding 10 MMBTU to the air. Sources of error on the air side are huge. We don't very often have air-flow measurement much better than +/-20%. We measure wall temperature and assume that it is representative (it rarely is). We don't measure the pressure on the air stream at the heater (makes a significant difference). We rarely account for the humidity of the air properly. Does all that add up to 50%? Very possibly.
David Simpson, PE
MuleShoe Engineering
"Belief" is the acceptance of an hypotheses in the absence of data.
"Prejudice" is having an opinion not supported by the preponderance of the data.
"Knowledge" is only found through the accumulation and analysis of data.
The plural of anecdote is not "data"
I wonder if what your saying about the air flow measurement being +/- 20% is playing a big role here. This is something that could be verified with a pitot tube, yes?
Fouling of the heater core does not affect the calculation that I would be doing for your problem. The fouling will simply require more mass flow for the same dS. You have calculated a dS and that calculation does not include any insulating effects within the heat exchanger, it is simply inlet enthalpy minus outlet enthalpy times mass flow rate.
David Simpson, PE
Post a simple diagram with steam flow, pressure and temp in and out and then someone more familiar with stream can tell you how much energy is going in and still coming out.
Zdas, the fan curve was calibrated for a specific temperature, density and elevation. I did not assume an RPM, I used the static pressure correlation on the fan curve to determine the CFM of air moving, its a fixed drive fan no belts. I can use the AMP readings to determine power.
I think it's backing up to the moisture in the system taking the extra energy.
- Steam might be condensing at exit and small droplet are carried with the flow.
- Air is not completely saturated, possibly the relative humidity is increased between air inlet and outlet.
Can it be that your system is combination of heat exchanger and condenser?
Maybe you should monitor the steam temperature and pressure at outlet and relative humidity of the air between inlet and outlet.
Question: where the steam goes when it exit the system?
There will be about 1,000 BTU of useable heat in each lb of steam.
(CFM X 1.08 X delta T)/1,000 = #/hr steam required.
This formula is from "Hook-Ups - Design Of Fluid Systems" by Spirax Sarco. I've used this thin, soft covered book for applications like this for 35 years, and it's never let me down.
If you really are using twice the steam that you figured, then you're moving twice the CFM, heating the air to twice the delta-T, or some combination of the two.
What I ended up doing when I originally calculated this was I looked at our flow tag that trends live on the DCS, assuming its accurate it says we flow 10,000+ lbs/hr of steam. I took this times the hfg of 150 psi steam (857 BTU/lb) to get the 10MM BTU/hr figure.
When I looked at the air side, I used the inlet and outlet temperatures for dT, and I used the static pressure on the calibrated fan curve to determine the mass rate (CFM of air). I used an average specific heat for Cp of the inlet/outlet temps. This came out to the 5MM BTU/hr figure.
I think what is occuring is alot of the steam energy is going into the specific humidity of the air stream, or water droplets in the air stream (its a closed loop ring dryer air is pulled off the top of the scrubber). This is causing much more energy to be put in to heat the water back up.
Rotaryw,
Steam goes to a condensate reciever.
Tom
I think a lot of your "lost" energy is flying out the other side of your HX as steam / hot water.
however maybe I've got the wrong end of the stick...