35kV cable distribution design for Wind Farms
Wind Farm Distribution Designers. I understand that low cost drives most wind farm installations, but, how can a common design used, where cables are buried, sometimes with splice boxes for cross bonding, for many miles with no access points available. Ten miles of buried 35kV cable with no accessible splice boxes prohibits the ability to use several of the most popular and effective means of testing the cables. The only test that can be performed, as a practical matter, is a VLF Withstand test to check the integrity of the system after installation. Even that test is impeded and made more expensive by the very long runs since the cable capacitance is so high. The design eliminates the ability to perform important diagnostic testing like Tan Delta/Power Factor and Partial Discharge. Also, the lengths designed make cable fault locating more difficult. Cross bonding neutrals with the boxes accessible and links to connect the neutrals in a phase continuous manner, so some tests can be done, is often not available.
In a nut shell, the typical design gives no consideration for the users ability to test or fault locate in an effective manner? How can this be changed to aid the owners/users of these systems? At least offer a way to access the cable every 3 - 4 miles.
RE: 35kV cable distribution design for Wind Farms
Most of the money is made from the goverment subsities that come with putting the whole thing in service.
http://www.pddnet.com/articles/2010/03/weakest-lin...
Any design engineering firms out there that care to jump in here?