Branch circuit or Feeder ?
3

Branch circuit or Feeder ?

Branch circuit or Feeder ?

(OP)
Hi,

My understanding from NEC 2011 article 100 is that: branch circuit conductor is connected between panelboard and receptacle, feeder conductor is connected between service equipment and panelboard. Regarding the conductor connected between a panelboard and its subpanel, is it a feeder conductor or a branch circuit conductor? I am asking because feeder and branch circuit have different voltage drop requirements. Thank you in advance.

RE: Branch circuit or Feeder ?

A feeder starts and ends at an overcurrent protective device.

RE: Branch circuit or Feeder ?

Per the NEC,what you described would be a feeder.

I thought the total 5% voltage drop fine print note can be any combination between branch and feeder as long as the total voltage drop was no more than 5%.

RE: Branch circuit or Feeder ?

Easier way to tell is that a branch terminates at the load device or receptacle. If it's not a branch, its a feeder (or service main).

"Will work for (the memory of) salami"

RE: Branch circuit or Feeder ?

shamsdebout,

Be careful when addressing voltage drop. I live in the U.S. and my state's building code mandates that voltage drop not exceed 2% for a feeder and 3% for a branch circuit. Based upon this requirement, a circuit with, for example, 4% voltage drop at the feeder and 1% voltage drop at the branch circuit, would be a violation.

RE: Branch circuit or Feeder ?

(OP)
jmbelectrical - Thanks for providing the building code information in your state. Building code mandates different voltage drops for feeder and branch circuit, that's exactly why I am asking this question.

I think the conductor between the panel and its subpanel should be a feeder based on my understanding of NEC and everyone's responses. Thank you all for providing suggestions.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources