Hi Everyone,

I have to condition a space which would be classified as non-occupant area. WSHP will be used for cooling and heating of that area. Do I have to provide an outside air for a space that will not be occupied at all? Equipment in the space requires conditioning of the area. Thank you!

RE: Ventilation requirements for non-occupant area

you could get better help if you would state what this area is. it looks like equipment area like computer room or similar.

if that is the case, you need to take care of two aspects:
- does equipment produce any kind of air pollution, like pollutant gases, dust etc.
- how maintenance work will be done, can door to adjacent space which is ventilated or large enough to have some "buffer" of clean air, be open during maintenance work.

RE: Ventilation requirements for non-occupant area

(OP)
Drazen,

In the equipment room there are two large electric units: pulse generator and AC/DC power supply. The equipment does not produce any air pollution. Equipment maintenance would be performed semiannually. Yes, the door can be open to the adjacent conditioned space.

RE: Ventilation requirements for non-occupant area

Per latest ASHRAE 62.1 (if that applies for you), all building spaces except IT and telephone closets should be ventilated at a minimum of 0.06 cfm/ft2. Other space types have a higher base cfm/ft2. If you want to classify the space as a "computer" room, there would be an additional 5 cfm per person with an occupant density of 4 per 1,000 ft2.

So if this room is 1,000 ft2, minimum ventilation would be:

(.06 * 1000) + (4 * 5) = 80 cfm.

RE: Ventilation requirements for non-occupant area

you have very precise chas' answer, and as you were mentioning definition of the space (occupied or not), i assume that's what you want to hear.

if legislation does not concern you (at least us legislation), than i would recommend that you take a look at generator manufacturer's documentation.

if none of it is binding you, you could possibly omit ventilation in such a space, as you neither have direct pollution, nor occupancy demands, not you need ventilation for heat rejection.

chas, do you have some one-page table of new ashrae 62.1 demands to link at? i know that 62.1 is much more than simple table, but i would like to compare it with older version of standard that i possess.

RE: Ventilation requirements for non-occupant area

YES, but not here at the moment. I'll post next time from work. Best to all, CB

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources