Chilled Beams Load Calculations in Trace 700
I'm trying to model a dedicated OA system with chilled beams in Trace 700. In Trace, this translates to a main cooling coil (the AHU or dedicated outside air system) and the auxiliary coil (the chilled beams). My problem is that I can't figure out how to set up the primary air conditions that I want. This is a custom DOAS, and we want to have the primary air delivered to the chilled beams at 58F DB, with 49 gr/lbs.
Usually I'd use the Dedicated OA tab in Trace to set the DOAS conditions, but for Chilled beams, adding a DOAS means you're adding another coil to the main and auxiliary, which we're not.
Does anyone here have experience doing load calcs on Trace with Chilled Beams?
RE: Chilled Beams Load Calculations in Trace 700
Is there a reason to deliver at 58°F this seems a tad too warm to dehumidfy, unless you use a secondary wheel (like in Semco Pinacle). You really need to dehumdify well for chilled beams.
costumary DOAS or not, wouldn't you regulate DOAS DAT with the same Building automation system?