Urgent Help! Reinforcing a Circular Slab with Metal Deck Form.
HI All
I have a circular suspended slab (23meters in diameter). The structure underneath is to be steel beam framing with metal deck over. The secondary beams are 90 degrees to the metal deck form. The primary beams are on the edges and the secondary beams frame into these. All top flanges are at the same level.
My analysis shows that top reo only is needed because the metal deck acts as bottom reo.
My question: How do I orientate the top reo?? I have shown a way on the attached(not sure if correct or practical).
I also have seen reo placed radially (for example water tank slab)...but I don't think it will work in this case since the metal deck profile is not radial - I could be wrong though!
My attached solution would mean that I would calculate the top reinforcement as a vectorial component.
Any ideas are welcome.
RE: Urgent Help! Reinforcing a Circular Slab with Metal Deck Form.
The vector components make sense.
Just to confirm there are edge beams on the perimeter ( which are not shown on my sketch). The overall diameter is 23m.
Not sure if I understand the "bottom bar" comments being made? The metal deck that I am using has ample capacity to do the job. Not that in my sketch the ribs are shown in black and the top mat of reo in red. My only concern is the top mat of reo.
Even if I do the vectorial sum method for the "As" in the top...how does one know that the angled bars are able to go back 0.3L ( which is normally the case for top reo. That is, As you have probably done in the past, negative reo( on the top) goes back 0.3L. If the bars are angled relative to the span...how do you get the 0.3L???
regards
I've seen many of these deck/slab assemblies tested in a lab and they all perform very well. In fact the variability/scatter of results is
about the same as shear failure in concrete beams.
Now using smooth formdeck -I would agree with you - don't count on natural bond between metal and concrete.
I would keep the top bars in orthogonal directions as you have shown. Much simpler to place that way. Where the bars are parallel to the deck, only one layer will work flexurally, so figure your "d" based on the lowest top bar. Where they are at 45 degrees to the deck, both work, with different effective depths. Don't separate it as suggested in your latest post. Too complicated, and losing continuity is not a good thing.
By the way, I would agree with Jed about the use of composite deck if this is in an environment where corrosion will be an issue, now or in the future. When composite deck corrodes substantially, there is usually no option but to demolish and reconstruct.
thanks mate. So essential work out the components of the top steel when not parallel to the deck.( which is what I first thought).
My only worry with that is the 0.3L fo rthe negative moment. This usually for steel in line with the moment diagram! now the steel is at an angle ( so does that mean more than 0.3L)?. Maybe it doesnt matter because I would be developing the bar at an angle instead of in line.
I did not explain it very well. The mat would be continuous in both directions. But if the mat is inclined to the metal deck, to comply with the 0.3 L requirement, this would not be achievable because the continuous bars are at an angle to the "0.3L" direction. i.e the 0.3L measured is in the direction of ribs...but the bars are at an angle to this.
I do personally think that it is largely irrelevant because the "0.3L" just needs to be satisfied in any direction and not necessarily in the direction of span of the deck.
Did that make sense?