PowerFlex 525 and 753 current rating.
PowerFlex 525 and 753 current rating.
(OP)
We have started using new families of Rockwell Automation drives, PowerFlex 525 and Powerflex 753. In the drives manual there is chart that showing drives input current rating and output current rating. On these charts output current rating is greater than input current rating.
It is opposite that in manuals for Fowerflex 40 and Powerflex 70. For these drives rated input current is greater than output rated current. It is kind of going alone with the fact that there will be some power losses, and resulting drive output current will be slightly less than input current.
When I ask that question technical support the answer was:
"here is the answer form engineering
The input current is a function of the power factor of the motor, the power factor of the power system and drive, and efficiencies of each part of the system. It is common to have a published output current higher than the input current for some drive ratings"
Is it really common to have rated output current higher than input current? How other drive manufacturers are rating ther drives?
PaulBr.
It is opposite that in manuals for Fowerflex 40 and Powerflex 70. For these drives rated input current is greater than output rated current. It is kind of going alone with the fact that there will be some power losses, and resulting drive output current will be slightly less than input current.
When I ask that question technical support the answer was:
"here is the answer form engineering
The input current is a function of the power factor of the motor, the power factor of the power system and drive, and efficiencies of each part of the system. It is common to have a published output current higher than the input current for some drive ratings"
Is it really common to have rated output current higher than input current? How other drive manufacturers are rating ther drives?
PaulBr.





RE: PowerFlex 525 and 753 current rating.
RE: PowerFlex 525 and 753 current rating.
A VFD essentially corrects the displacement power factor of the motor as seen by the drive. So if the motor PF is .8, and the input PF to the drive is .95, then the input amps will be lower.
"Will work for (the memory of) salami"
RE: PowerFlex 525 and 753 current rating.
"Will work for (the memory of) salami"
RE: PowerFlex 525 and 753 current rating.
I've actually noticed it with PowerFlex 525. Frame D and E of 380-460V all have output current higher than input current.
PaulBr.
RE: PowerFlex 525 and 753 current rating.
It is like that on the 575V version though.