Heat exchanger Evaluation
I have a shell&tube heat exchanger with 15% of tubes plugged!! How Can enusre that exchanger is still safe to operate? is there any sort of calculation that I can perform?
Heat exchanger EvaluationHeat exchanger Evaluation(OP)
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesThe world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
Engineering-centric businesses face a number of challenges today, but unmanageable design and change processes don’t need to be counted among them. Download Now
RE: Heat exchanger Evaluation
You need to check whether the remaining area of your heat exchanger can still meet the duty of the services (be it out let temperature etc.). You can use any of the available exchanger simulation tools in rating mode to estimate the exchanger performance. What might also be worthwhile to check, is your new tube side velocity after plugging the tubes. Check if the new velocity is still within the allowable operating range and no excessive pressure drop is experienced. I hope this helps.
Cheers,
gr2vessels
The tubes were initially plugged as a result of a recent shut down and due to fouling of produced water, and now they are completely sealed with tapper plugs. The expectation is that some form of engineering calculation be documented on record.
This is how I am planning to do my calculations:
Q= UA (ΔTlog mean)
I assume (ΔTlog mean ) changes will be negligible. I will calculate “U(new with 15% tubes plugged)” and “A (new with 15% tubes)”.
Knowing “Q (old with no tube plugging)”, New heat duty can be calculated by writing a ratio between heat duty old and heat duty new:
Q (old with no tube plugging) /Q (new with 15% tubes plugged) = U (old).A (old)/ U(new).A(new)
And then the outlet temperature (t2) can be calculated from equation:
Q(new) = m.c.(t2- t1)
Using equation for pressure drop (found in the literature) and velocity equation I can calculate the new velocity as well as the pressure drop.
But then I have to compare these values with the acceptable design values!! However, I don’t know what’s the acceptable design values !!
Can you guys please give me a feed back for my calculation and tell me in you know the acceptable values for pressure drop, velocity, heat duty and temperature.
LOL. Is the unit operating now? You are doing to see two things with 15% of your tubes plugged, outlet temperatures will be higher than they were previously unless it's a constant temperature process on one side such as steam condensing and tube side pressure drops will be higher (the dP should be about 30% greater than it was before the tubes were plugged).
I'm going to assume you have access to operating data while the exchanger was in service prior to this work. Calculate the Q and the dTlm. You know the original area so you can calculate the overall heat transfer coefficient. If it's not been returned to service, I'd likely assume UA is constant and solve for the new dT log mean and see what that means for outlet temperatures. Decide if the higher temperatures (see the above caveat) is acceptable. If the unit is already back in service, compare your numbers to the actual field data as a check and make your evaluation if the operation is acceptable.
< and tell me in you know the acceptable values for pressure drop, velocity, heat duty and temperature >
Depends on your system. There's no way anyone can give you specific limits when you've provided no real information.
