I work for an electric utility in Oklahoma. Our Design Standards department is trying to tell me that a residential air conditioner has a starting power factor of .35 lag. I find this hard to believe. This results in almost four volts of flicker drop in a 25 kVA transformer. Does anyone know the typical starting power factor for an air conditioner motor? Is the starting power factor for a reciprocating compressor motor different than the pf of a scroll compressor motor? If anyone knows where I can find this type of information I will be glad to go look it up. I searched ARI (American Refrigeration Institue) but had no luck finding anything pertinate. Thanks.






RE: Starting Power Factor of Air Conditioner Motors
Have you checked with motor manufacturers? They should have this data.
The information is 37 years old, but FWIW my 1965 copy of the Westinghouse Distribution Systems book lists exactly the information you are looking for in Tables 4 and 5 of Chapter 2.
RE: Starting Power Factor of Air Conditioner Motors
In fact, the IEEE Red Book identifies a typical starting power factor of 0.2.
Look at the equivalent circuit. The only significant resistive component is R2/s. When s is high that component becomes less important and inductive elements dominate.
RE: Starting Power Factor of Air Conditioner Motors
Title: The effects of distribution system parameters on air conditioning motor startup flicker. Year: 1999?
Charlie took actual field measurements of voltage and power factor for both piston (reciprocating) and scroll compressor motors. Table 1 of the paper shows that most air conditioners have as low as 0.70 and as high as .95 starting power factor. I'll take actual field measurements any day.
Thanks again for your help.
RE: Starting Power Factor of Air Conditioner Motors
I don't know for sure but I would guess there are likely some split phase motors used in residential air conditioning which don't use starting caps and will have much lower power factor in the 0.2-0.3 range.
RE: Starting Power Factor of Air Conditioner Motors
RE: Starting Power Factor of Air Conditioner Motors
RE: Starting Power Factor of Air Conditioner Motors
You're right, I knew that. I just don't bother with it. Worst case is when the impedance of the starting motor (which is also primarily inductive) is exactly in phase with the source impedance. Make that assumption, and impedances add up numerically making life much simpler.
If that approximation doesn't suite, the T&D Reference Book has a different one: 6X FLA at 35% pf.