I have heard several times that ductwork in power plants should be designed for +/- 35" H20 pressure. Can someone point me to the NFPA standard and section where that requirement is mentioned?

Is the 35" requirement in addition to other design loads (i.e. dead load, live load, wind load, etc...)?

Thanks,

RE: Power Plant Ductwork Design

(OP)
Update, I located the section in NFPA 85 I was looking for. I believe they are actually saying the duct need NOT be designed for more than 35", but should at least be designed for the test block capabilities of the fan (if less than 35").

The section is uploaded here:

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources