Joints in Concrete Equipment Slab?

Joints in Concrete Equipment Slab?

Joints in Concrete Equipment Slab?

(OP)
I have a 60' x 16' x 8" thick reinforced concrete equipment slab on grade (exterior) that will be supporting electrical equipment. I want to put control joints in the slab because of the length to width differential. I considered saw cutting control joints but I will only be able to provide a joint that is approx 3/4" deep because of the top reinforcing (yes, it needs it). I considered dividing the pad into 3 isolated sections, separated by expansion joints, but this will cause issues with the equipment anchors - there are many pieces of equipment and the anchorage points are freqent.

1. Do you think the pad needs joints?
2. If yes, do you think a 3/4" saw cut will be sufficient depth to be an effective control joint? If not, do you have any suggestions?

Thanks!

RE: Joints in Concrete Equipment Slab?

If you have enough reinforcement to control the cracks, why would they be a problem? They might not be straight like a sawn crack, but for an equipment pad, they would not affect serviceability. I doubt that a 3/4" deep sawcut would force the crack to occur at that location.

RE: Joints in Concrete Equipment Slab?

No point putting an expansion joint in if the reinforcement is running through the joint, Only time this would work, for example if you had slab on grade and mesh for crack control cutting every second reinforcement bar segment through the saw joint and then cutting the slab will give you a joint. However you will still need better detailed joints every 3-4 saw joints.

You need to weaken the reinforcement in the location of the saw cut otherwise it wont work. The slab you are doing is very small and i would not see it as an issue, if you are concerned place more reinforcement in the long direction to control shrinkage in this direction.

RE: Joints in Concrete Equipment Slab?

Cracks in reinforced slabs are purely aesthetic and have no functional detriment other than a pathway of water to rebar.
Go ahead and sawcut the joints to the rebar depth. This will help (but not completely) control cracks in the concrete. Sawcuts in reinforced slabs need to be relatively close together (seems intuitively opposite...but not)....keeping in mind you are controlling crack appearance in a highly restrained surface.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources