knee brace
knee brace
knee brace
I'm having trouble with a rooftop equipment frame with knees braces on my post down. I'm posting down on columns and using pin connection with knee braces to avoid a fixed end (the roof slab is only 2 1/2 inches on concrete on a 3 inch deck). The issue is that the knee braces carry the gravity load into the posts and blowing the posts out. But if I don't put knee braces in my frame deflects like crazy. Is there a way in RISA to only have the knee brace act as a lateral brace and not transfer gravity loads?
RE: knee brace
I cannot think of a way to do this. If the brace prevents the beam from deflecting vertically, then it doesn't care whether the deflection comes from gravity load or lateral load. Isn't that what you want the analysis to tell you? How the structure is actually behaving under the applied load. Perhaps rather than adjusting your model, you need to beef up those columns so that they can take the gravity load.
Could this be a case where the gravity loads are already present in your structure (with the beam deflected as a simply supported beam). And, you are just adding the knee braces to the existing structure.... Sort of a staged construction. Where the gravity loads act on the un-reinforced frame. And, any additional load (i.e. lateral load) would attributed to the reinforced frame. That's a non-linear type of analysis that RISA doesn't do automatically. However, you can manage it by manually combining the results from different models.
For example, you could eliminate the gravity load from the beam and just attribute it directly to the column. Then run the beam design in a separate analysis and use superposition to combine the beam results together.