Modulus of Subgrade Reaction - Geometrically standard - Reduction for larger areas
From the geotech report for Mat slab:
A modulus of subrade reaction is given for a 30" diameter load plate = 200pci. However it is then stated that "depending on how the slab loads are applied, the value will have to be geometrically standard. The value should be adjusted for larger areas using the following expression for cohesionless soil:"
ks = k* [(B+1) / (2*B)]^2
Where
B = width of the loaded area, in feet
k = coefficient of vertical subgrade reaction for 707 in^2 loaded area
ks = coefficient of vertical subgrade reaction for loaded area
Questions:
1. Can someone help me understand what this is for or how it is applied?
2. What direction is the loaded area intended to be (i.e. the larger of the 2 directions if you have a rectangle)?
3. why is it being referred to as a coefficient now?
Say I have a 50' x 80' rectangular mat should the subgrade modulus be
k = 200*[(80+1)/(2*80)]^2 = 51.25 pci ?
Also why not provide a subgrade modulus that varies based location in the mat (i.e. higher at edges than at center or vice versa I can't remember which is correct).
Where
Questions:
RE: Modulus of Subgrade Reaction - Geometrically standard - Reduction for larger areas
This topic is too involved to cover it here in detail. The following two books will help you get started:
Foundation Analysis by R. F. Scott, 1981
Design & Performance of Mat Foundations, SP-152, ACI, 1995
In general, this vertical subgrade modulus method has many limitations and can be on the unconservative side if you have 3 or more column lines. Changing the Kv value by 300% will not affect your induced bearing pressure, shears and moments by more than 5%. Also as you have noticed, you have to assume one Kv value under the entire beam strip length. So what happens when the soil is stiff clay one the east side and loose silty sand on the west side of the building - is it rational to use the same Kv value? Further, how can you depend on a method that, in general, when input parameters are tripled, the output values are nearly unaffected?
That is why back in 1975, researched Lee, discouraged the use of this method. Dr. Poulos emphasized the same thing in his 2000 Buchanan lecture - see attached excerpt.
So where does this leave you? Try to get books that explain the Continuum method of raft foundation design.
It's an equation from Plate Bearing Test by Terzaghi. Modulus subgrade reaction ks is conceptual only, not soil parameter.
The story began when Terzaghi tried to relate the vertical deflection (d) of a shallow foundation to the load that applied on that foundation (q). Then he defined the relation as ks = load q / deflection d.
The test was performed on a certain size area of plate (on you case the plate is circular plate of 2.5 feet diameter, British standard), so a conversion is needed to use this ks for different sizes of plates / foundations.
The equation ks = k* [(B+1) / (2*B)]^2 from your Geotech report is for squared area B (width) = L (length)
For rectangle area the equation will be : ks = k* [ (m + 0.5) / 1.5 m ] where m = L / B and L > B
Hope that would help.
Cheers.
Thanks for the info. I would like to look into the Continuum method of raft foundation design, any references in mind?
I read through Scott and Bowels and was left thinking that they would have us vary the Subgrade Modulus based on the location underneath the mat (i.e. near center vs edge). Either Scott or Bowels mentions this. This is where most of my confusion was.
@Andre -
Thanks for the info. That makes sense, as I mentioned I was expecting some sort of equation to vary the Subgrade based on location. But it seems as though I will have a constant subgrade below the entire mat. Which I guess makes it easier for me. As all the springs are now the same (if I have a regular sized mesh in my FE model).
Thanks again!
EIT
www.HowToEngineer.com
The continuum method use the soil's "E" and "v" parameters. Since predicting the accuracy of "E" value for soil can be dificult, you need to check the reasonableness of your settlement and moment output. On your first few jobs, consult with experienced mat foundation designers.
He also describes a rigorous method to apply in mat foundations, which once I suggested to the structurist but apparently it is not immediately applicable in the commercial structural softwares, requiring separate FEM software.
EIT
http://www.youtube.com/watch?v=M1xCE09mpTY
Clearly describes how the "k" value should be determined.
http://jshce.com/files/ceenge-2011-1.pdf
As soon as I read it I sent it to a structural engineer who was willing to try it out. He told me that his commercial structural software (and most likely all Others) couldn't apply the method although he could have used separate standalone applications.
Which wasn't good news, since structural guys ask for winkler data immediately applicable in their structural softwares.
EIT
Althou I have to say that I have also truble understanding when the talk aboth interation proce between geotehnical and strucural engineer (around time 28:50 in the video).
Can anyone comment?
The iteration procedure simulates the ridistribution of stresses in function of different loading configurations and time elapsed if I'm not wrong here.
Agree that the presentations is impressive