Dry Pipe Valve Location
Here is my situation:
I have a standpipe riser located in the stair. At the top of the standpipe riser, where a cap is normally found, the Contractor has installed a dry pipe valve in line with the riser. The dry pipe valve feeds the dry system on the roof.
Although this is an odd place for a dry pipe valve, I see it as no different than installing a horizontal floor control assembly off the riser for the top floor.
Any thoughts on this. 2010 edition of NFPA 13 and 14.
I tried to post a pic but it doesnt work! (or I just dont know how)
Thank you!!
RE: Dry Pipe Valve Location
Easy to reach and work on?
Can fireman reach it with ease?
Heated area I assume
Yes
Yes
Correct assumption.
I've seen this several times. Nothing wrong with it, provided they have the drains to handle draining the system.
Travis Mack
MFP Design, LLC
www.mfpdesign.com