Perimeter Heat
Perimeter Heat
(OP)
I am trying to remember amount of exterior wall heat loss per foot (btu/ft) when perimeter heat (finned tube, radiant panels, etc.) should be used to supplement overhead heat. I know it is somewhere in ASHRAE but I cannot find it. Can you help me? This is for a health care application.





RE: Perimeter Heat
You could get away without perimeter heat if:
- you are in moderate climate (not less than 20°F in winter (I'm just makign up these numbers)
- and if yoru envelope is very good (R25, no windows or really really small and good ones.
Anything else I would recommend perimeter heat. Besides being more comfortable, it also prevents you from running AHU during off-time.
Once you have perimeter heat, you probably want to size it to cover most if not all of the perimeter losses.
Regardless of application (healthcare, office...), you need to make people comfortable. Ceiling based VAV with slot diffusers really has a hard time heating, is noisy, drafty, and inefficient.
RE: Perimeter Heat
RE: Perimeter Heat
RE: Perimeter Heat
In cold climates, ie, temps <30F, counteracting downdraft is best done by a heat source under the wall......heat rises and blowing sir down from the ceiling does not do the trick.
RE: Perimeter Heat
as willard mentioned, there is high probability of local drafts if temperature difference between outdoor and indoor space is too high.
this depends both on your climate and level of insulation.
there is currently a new "school" of green design which advocates avoiding perimeter heating wherever possible, but i'm not fan of it.
you should also tell us about type of spaces you have at perimeter.
in general, though, hospitals deserve more conservative approach than other types of buildings.
RE: Perimeter Heat
RE: Perimeter Heat
Also near entrance doors you have more infiltration and perimeter heat is needed.
I think roomheight is important. An 8ft ceiling may work with ceiling diffusers, a10' won't. If in doubt, use perimeter heat.
We have many buildings in WI. Some w/o perimeter heat, some with. Guess which ones have the comfort complaints in winter?
Even whne Trane has a certain repertoire of products, their advice is very neutral. i never had the impression they lie to sell me something.
RE: Perimeter Heat
RE: Perimeter Heat
but I found compared to all other manufacturers their advice is most neutral. All their technical papers, seminars etc. are very professional and sophisticated. They are applicable to Trane equipment, but also to Carrier etc.
in the end the engineer still needs to use his own brain :)