Disconnect Switch Replacement

Disconnect Switch Replacement

Disconnect Switch Replacement

(OP)
This is my first time working on a disconnect switch replacement project for a local client. The high of the existing disconnect is 21 FT and that is from the top of its foundation to the center line of the disconnect 4-hole pad (as well as the center line of the bus). The new switch is 0.125 inches higher so I am unsure how to transition from the bus which is at 21 FT to the disconnected terminal which is .125 higher. Can anybody suggest any ideas?

Thanks in advanced.

RE: Disconnect Switch Replacement

Can you tell us voltage, amps, bus dimensions?

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies

RE: Disconnect Switch Replacement

(OP)
The voltage level is 345KV, 3000A, bus 5", bus high 21FT. Thanks

RE: Disconnect Switch Replacement

Drill all connecting holes out another 0.0625 inches. There may already be enough clearance in the bolt holes to bolt up without extra drilling.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Disconnect Switch Replacement

I don't think that the centerline of the old disconnect terminal would be at the same height as the centerline of the bus. If the bus terminal connector is center-formed and placed on top of the switch pad, the bottom side of the bus terminal (center of bus) would be at the same height as the top of the switch pad, not the center of the pad. If it was placed on the bottom of the switch pad, the top side of the bus terminal (center of bus) would be at the same height as the bottom of the switch pad. If the bus terminal were not center-formed, the center of the bus would be offset from the switch terminal pad.

In any case, unless the connecting bus is very short, it wouldn't have to bend much to make up for 1/8" of height difference.

I'm assuming a horizontally mounted switch and horizontal bus. Waross must be considering vertical mounting.

RE: Disconnect Switch Replacement

We use flex linjs from ips to switch. Have you made a field inspection ?

RE: Disconnect Switch Replacement

If it is horizontal mount, rotsing column and fixed column all have leveling bolts, and should be movable up or down by the amount stated. Please see instalation manual ninimum / maximum height. Your maybe the median if taken of a spec sheet.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources