Prestressed beam weight for crane lifting - a practical or theoretical approach?
Hi there,
I'm in a bit of a dilemma. Two arguments for the self weight of a beam.
1. to take a standard 2500kg/m^3 for the beam as (unit weight)which would include for the steel. for a beam with theoretical volume of 20m^3
so 2500*20/1000 = 50tons
or
2. take the cylinder tested density of 2430kg/m^3, the steel strands 1.1tons, the actual steel weight 8.9tons and miscl.of 2 tons for grout, collars etc.
2430*20/1000+1.1+8.9+2 = 60.6tons.
problem
1, in calculation 1, the density is underestimated as the steel is much denser, as is the concrete.
2. in calculation 2, the steel hasn't been taken out of the concrete.
Problem,
For a crane lift it is obvious you want to be as conservative as possible. Do you:
1. take calculation 1 as a blanket calculation and risk underestimating the load, or,
2. factor everything in and give yourself a bit of legroom?
What is the standard, or best approach?
I would really appreciate the thoughts and input on this!
or
problem
Problem,
RE: Prestressed beam weight for crane lifting - a practical or theoretical approach?
BA
Michael.
"Science adjusts its views based on what's observed. Faith is the denial of observation so that belief can be preserved." ~ Tim Minchin
(Area of concrete - Area of rebar) * Length * Density of concrete + Area of steel * Length * Density of Steel
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
And the grout is filling voids in the cross section, so no need to add that, unless you deducted the ducts when calculating the concrete volume.
Doug Jenkins
The beam has a lot of steel in it.
2430*20/1000+1.1+8.9+2 = 60.6tons."
You likely overestimated re-bar weight. For well design beams rebar to concrete ratio is about 1-1.5%, and for columns around 2.5-3.5%. 4% is a practical limit. In your case you have appx. 5.6% (for longitudinal bars only).
So if we assume 1.5% rebar, 0.015 x 7850 kg/m3 x 20m = 2.36 t, add 30% for ties, overlap etc 3.10 t steel. Thus 2430*20/1000 + 3.1 = 51.7t which is the same for all practical purposes to estimated 50t.
The steel weight is known. This is from delivery tickets (fabricators slips)this isn't underestimated, its a heavily reinforced highway bridge beam 8.9Tons.
The tested dry density is known and a little higher than normal OPC concrete 2430kg/m^3.
The volume of the concrete is known from the delivery notes. This is higher than the theoretical by 4m^3.
So if I know the volume of concrete that went in by the concrete tickets(this is the displaced volume), I know the weights of steel etc. surely this is the way to go.
Multiplying the theoretical volume by 2500kg/m^3 is this not underestimating the load?
But I'd still suggest checking that the reinforcement weight is not in kN, rather than tonnes (or maybe that the weight supplied is for 10 beams rather than one). Also where has all the extra concrete gone if the actual volume is 20% higher than the theoretical?
Doug Jenkins
"displaced volume? a known volume and the difference between..what exactly? displaced means you know the volume of a bath. although you fill it an what spills out is the displaced volume. so I don't think your getting this." ---> He is definitely getting it. Water in bath = concrete in beam, you = rebar. Rebar displaces concrete. Go take a bath and pretend you're a piece of steel, you'll get it.
I would think the most accurate way to get the concrete volume is to measure the actual finished dimensions of the beam to get the volume and then subtract your known volume of steel.
IMHO, put aside your detailed assumptions and calculations and go the documentation on the prestressed beam design. In the USA, that is the "Precast / Prestressed Concrete Institute" (PCI). Check their tables on the type beam of interest:
http://www.pci.org/Design_Resources/Transportation...
For the various shapes the nominal weight is given in kips / foot.
If you are not in the US, perhaps you have a similar governing body to consult.
Then, spend the time saved making sure that the lift plan makes sense, the lifting equipment is of adequate capacity and in satisfactory condition. Because of possible unintended loading during the lift, this is far more important than a calculation of the beam's precise weight.
www.SlideRuleEra.net
www.VacuumTubeEra.net
Caneit, thank you for your reply, your approach isn't very practical as it's a 30m beam of irregular shape which tapers. Why work out the volumes when you know what's been paid for? I think the known factor here is what's been delivered, I have known placed volumes of concrete, and known steel weights. I think that's the best approach. Then applying a shock load factor to check the ancillaries. There are 72 beams all complete and we have the placed volumes in each.
Slideruleera- I will check out the site, thanks for the link.
It sounds to me like you are trying to avoid calculating the volume of the concrete beam. You could have done this calculation in less time than it took you to write and read all of these responses.
www.PeirceEngineering.com
if you work it this way, (without having to measure the beam)
Steel is 7850kg/m^3
our tested dry density is 2430kg/m^3
Ratio of concrete to steel is 3.23.
Theoretical volume is 20m^3
Steel is 8.9Tons
Therefore 8.98*1000/20 gives you 445kg/m^3 of steel
Which is 445/3.23 = 137.77kg/m^3 of concrete to deduct.
137.77*20 = 2755kg or (2.755Tons) has to be deducted
as I used in (2) way at the start of the thread (above) the theoretical volume, If I deduct the steel 60.6-2.755 = 57.85Tons
This I would say is the real beam weight, though for safety sake, I would have left the 2.755 tons in the original calulation.
Still way higher than a blanket calculation using 2500kg/m^3 unit weight......Anyone disagree?
Theoretical Volume of Beam = 20 m^3
Mass of Steel = 8900kg + 1100kg = 10000kg
Density of Steel = 7850 kg/m^3
Volume of Steel = 1.274 m^3
Volume of Concrete = 20 - 1.274 = 18.726 m^3
Theoretical Density of Concrete = 2500 kg/m^3
Theoretical Mass of Concrete = 18.726*2500 = 46815 kg
Theoretical Mass of Beam = 46815 + 10000 = 56815 kg
Actual Density of Concrete = 2430 kg/m^3
Actual Mass of Concrete = 18.726*2430 = 45504 kg
Actual Mass of Beam = 46815 + 10000 = 55504 kg
I may have interpreted it wrong, but when you said you had an extra 4 m^3 of concrete I took that to mean an extra 4 m^3 per beam. The only way that is possible is if your beams where significantly larger. If its an extra 4 m^3 for all 72 beams than that is only a difference of .3%
http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
I agree with the method you have followed (though I haven't run the numbers on the calculations to see that they are correct), but from experience I would just take the density of the beam as 26kN/m^3 and call it a day.
If the steel density is really as high as stated then the beam weight should definitely be adjusted to allow for that. It's not as though it's a difficult calculation.
Doug Jenkins
BA
Oops! Yes, I meant 520 kN.
I wish we could use force units for weight, but as the people who handle and transport heavy things think in tonnes I guess we are stuck with it.
How does it work in Canada? Are lifting loads given in tonnes, or tons, or what?
Doug Jenkins
BA
This whole thread seems to be an exercise in assumed precising relating to the actual weight of the elements to be erected.
When designing, engineers make assumptions of the loads on the conservative side to cover possibilities.
For a contractor to be given precise weights seems to be a futile goal, since in the end, all of the 72 elements will probable be set using the same crane/cranes unless there are some radical differences in the assumed weights and the geometry /angles needed for erection. Normally a crane is selected as being adequate and AVAILABLE depending on the construction process and schedule. The crane capacity (minimum plus 20 10 or 20 tons)and to be selected will be determined by the contractor unless you want to give precise weight and accept the liability of future results. - It makes little sense to schedule, move in and set up different cranes for minor differences in element weights.
Usually the contractor is the one that has to be concerned with the end result ot the erection and placement, unless someone wants to give precise weights.
Dick
Engineer and international traveler interested in construction techniques, problems and proper design.
BA
Dick,
The calculation of the girder weight is simple and doesn't take long at all.
You already know;
1. The theoretical volume.
2. The weight of the steel, strands, ducts etc.from supplier notes.
3. The tested concrete density.
4. The steel density.
What if your actual weight is several tons over the assumed weight and your safety factor takes you over the capacity of some of the lifting ancillaries...wasn't is best to check the assumed against the actual then?
BA,
These are site fabricated beams otherwise that would certainly have been the preferred solution.
I agree you have to assume weights for design. My point is once the structure has been built you find that the weights are higher than assumed, can be a problem.
Checks on tested densities and actual steel weights need to be carried out in case the assumptions were wrong. Particularly for critical lifts, which is the case we found.
I read a few articles on this saying that in reality the actual weights were almost always lower due to assumed weights being conservative. Statements like that are crazy and misleading as you should always use common sense and be mindful of what your steel% and concrete spec. actually is.
In our case the loads were found to be higher after checking.
Anyone disagree?
When we do the design for heavy lifts we make a number of assumptions as part of the design process but before we lift anything we will have the item weighed. Especially if we are going to be close to the capacity of the crane.
Weighing will be the thing to do in this case.