Unbalanced Delta Transformer Loading

Unbalanced Delta Transformer Loading

Unbalanced Delta Transformer Loading

(OP)
Hello. Looking for educational assistance understanding unbalanced loading. Connected to the output of a 415V 3Ph Delta transformer are the following kW values and p.f.s: Ph AB 3kW,0.8pf; Ph CA 5kW, 0.7pf; and Ph BC 7kW, 0.6pf.
Looking for assistance calculating the line currents IA, IB, and IC.

I started breaking the components out for each phase and arrived at (I think)
Ph AB: Iab = 9A at 53deg (7.2+5.4i)
Ph CA: Ica = 17A at 164deg (12.0+12.3i)
Ph BC: Ibc = 28A at -83deg (16.8+22.5i)

IA = Iab – Ica
IB = Ibc – Iab
IC = Ica – Ibc

RE: Unbalanced Delta Transformer Loading

You've done it, assuming that Vab = 415 at 90deg, except that your polar to rectangular conversions are wrong.
9 at 53deg = 5.4 + 7.2i
17 at 164deg = -16.3 + 4.7i
28 at -83deg = 3.4 - 27.8i

All you need to do is finish the math.
IA = (5.4 + 16.3) + (7.2 - 4.7)i = 21.7 + 2.5i = 21.8 at 6.6deg
IB = (3.4 - 5.4) + (-27.8 - 7.2)i = -2 - 35i = 35.1 at -93.3deg
IC = (-16.3 - 3.4) + (4.7 + 27.8)i = -19.7 + 32.5i = 38 at 121.2deg

RE: Unbalanced Delta Transformer Loading

(OP)
I am now most confused.

3kW/0.8pf = 3.75kVA
3kW*1000/415V = 7.2A real; 3.75kVA*1000*sqrt(1-0.8^2)/(415V) = 5.4A reactive
7.2 + 5.4i : Sqrt(7.2^2 + 5.4^2) = 9 ; Cos-1(7.2/9) = 53deg

How are you developing the components for phases BC and CA?

RE: Unbalanced Delta Transformer Loading

(OP)
Nevermind, I figured out the other two phases and how you generated them. Once the magnitude is known, determining the other components is easy. Came clear once I drew the diagram.

Once determining the magnitude of the phase amps then the following is clear

17 cos(164) = -16.3 : 17 sin(164) = 4.7
28 cos(277) = 3.4 : 28 sin(277) = -27.8

RE: Unbalanced Delta Transformer Loading

It is important if the pf is leading or lagging the voltage. If it lags then imaginary part has to be negative.
IAB=7.22-5.43j .But in any case the angle has to be +/- 36.87 dgr.[if the entire circle of 2*pi=360dgr.].
ACOS(0.8)=ATAN(5.42/7.22)=0.6435 radians=0.6435*180/pi()=36.87 dgr.

RE: Unbalanced Delta Transformer Loading

where did I make mistake?

If we assume three phase transformer phasor group Yd1 or Yd11, ABC phase sequence,
Voltage reference is VBC
PhAB=[3 0.8];% P pf; [kW cosfi]
PhBC=[7 0.6];
PhCA=[5 0.7];
VAB= 0.415;% kV
VBC=VAB,VCA=VBC;


a=cos(2*pi/3)+j*sin(2*pi/3);
disp('***************** EXIT')
tetaBC= acos(PhBC(2)); %rad
QBC= PhBC(1)* tan(tetaBC);%kVAr
NBC=sqrt(PhBC(1)^2 + QBC^2); %kVA

IBC = (PhBC(1) + QBC*j)/ VBC %A /0
%IBC = 16.8675 +22.4900i ; % A

% or

IBC = (PhBC(1) + QBC*j)/ j*VBC %A /90
%IBC = 3.8733 - 2.9050i; % A


RE: Unbalanced Delta Transformer Loading

If the angle origin is in VBC then IBC=16.87+/-22.49 and the angle is 53.13 dgr. indeed. I took VAB as origine.
Power factors are usually stated as "leading" or "lagging" to show the sign of the phase angle.
Capacitive loads are leading (current leads voltage), and inductive loads are lagging (current lags voltage).

RE: Unbalanced Delta Transformer Loading


where did I make mistake?


a=cos(2*pi/3)+j*sin(2*pi/3);
disp('***************** EXIT')
tetaBC= acos(PhBC(2)); %rad
QBC= PhBC(1)* tan(tetaBC);%kVAr
NBC=sqrt(PhBC(1)^2 + QBC^2); %kVA
IBC = (PhBC(1) + QBC*j)/ VBC %A /0
%IBC = 16.8675 +22.4900i ; % A


tetaAB= acos(PhAB(2)); %rad
QAB= PhAB(1)* tan(tetaAB);%kVAr
NAB=sqrt(PhAB(1)^2 + QAB^2); %kVA
IAB = (PhAB(1) + QAB*j)/ a*VBC %A +120
IAB = 0.1862 - 1.5451i; %A


tetaCA= acos(PhCA(2)); %rad
QCA= PhCA(1)* tan(tetaCA);%kVAr
NCA = sqrt(PhCA(1)^2 + QCA^2); %kVA
ICA = (PhCA(1) + QCA*j)/ -a*VBC %A /-120
ICA = -0.7958 + 2.8555i; %A

RE: Unbalanced Delta Transformer Loading

I don't know your software language. I do the calculations only on Excel [Microsoft-Office 2010]-or VB6.
However if your reference voltage is VBC [VCA=a*VBC,VAB=a^2*VBC] for inductive reactive power:
IBC=16.87-22.49*j ; ICA=-16.67-4.29*j ; IAB=1.08+8.97*j
if VAB will be the reference and the phase order will be AB,BC,CA then:
IAB=7.23-5.42*j ; IBC=-27.9-3.36*j ; ICA=4.62+16.58*j
If reference will be -90 dgr[-pi()/2] and the phase order will be AB,BC,CA then:
IAB=+5.42+7.23*j; IBC=3.36-27.91*j ;ICA=-16.58+4.62*j –as jghrist said.

RE: Unbalanced Delta Transformer Loading

When a delta transformer is loaded with a single phase load, all three phases contribute.
For a single phase unity power factor load on AB, the current In each winding of the supply transformer will be equal and equal to 50% of the load current. The current in the in-phase winding will be at unity power factor.
The current in one phase will be 60 degrees leading (50% PF) and the current in the third winding will be 60 degrees lagging (50% PF).
To understand this consider a three transformer bank split into an open delta (broken delta in IEC land) and a single phase transformer.
The virtual single phase transformer formed by the open delta may have its values described by the resultant vectors of the addition of the vector descriptions of the two real transformers.
These resultant vectors will be equal to the vectors of the transformer that was removed.
What I am trying to say is that for the case of a single phase load on a delta transformer bank, the transformer bank may be considered to be a real transformer in parallel with the virtual transformer formed by the open delta. The real transformer and the virtual transformer will share the load equally (assuming three identical transformers forming the delta bank).
In the case of a wye delta transformer bank with the primary neutral connected, these currents will be reflected in the three independent primary currents.
Now if the three transformers have different PU impedances and/or are rated on different KVA bases, the division of the current is a little more difficult to solve.
If a solution for one single phase load on phase A-B does not show a current on C phase the solution is incorrect.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Unbalanced Delta Transformer Loading

PhAB=[3 0.8];% P pf; [kW cosfi]
PhBC=[7 0.6];
PhCA=[5 0.7];
VAB= 0.415;% kV
VBC=VAB,VCA=VBC;

% an inductive load has a lagging power factor,the capacitive load
% has a leading power factor, resistive load has a unity power factor
% we assume 3phase voltage balanced, AB,BC,CA phase order, with inductive load(P-jQ) relative to voltage associated,
[

%for AB,BC,CA phase order VBC reference
a=cos(2*pi/3)+j*sin(2*pi/3);
VBC= 0.415;
VCA= a*VBC;
VAB= a^2*VBC;
clc
disp('***************** * SAIDA-VBC reference')
tetaBC= acos(PhBC(2)); %rad
QBC= PhBC(1)* tan(tetaBC);%kVAr
IBC = (PhBC(1) - QBC*j)/ VBC; %A

tetaCA= acos(PhCA(2)); %rad
QCA= PhCA(1)* tan(tetaCA);%kVAr
ICA = (PhCA(1) - QCA*j)/VCA; %A

tetaAB= acos(PhAB(2)); %rad
QAB= PhAB(1)* tan(tetaAB);%kVAr
IAB = (PhAB(1) - QAB*j)/ VAB; %A

IA = IAB - ICA ;
disp({'modIA angIA' abs(IA),angle(IA)*180/pi})
IB = IBC - IAB;
disp({'modIB angIB' abs(IB),angle(IB)*180/pi})
IC = ICA - IBC;
disp({'modIC angIC' abs(IC),angle(IC)*180/pi})


***************** * EXIT for VBA,VBC or VCA as reference
'modIA angIA' [22.1556] [36.7605]
'modIB angIB' [35.1998] [-63.3534]
'modIC angIC' [38.1575] [151.5093]

%%%%%% jghrist calculation
% IA = 21.8 at 6.6deg
% IB = 35.1 at -93.3deg
% IC = 38 at 121.2deg

RE: Unbalanced Delta Transformer Loading

odlanor, your calculation is correct, this time.

RE: Unbalanced Delta Transformer Loading

My calculation assumed that the OP Ø-Ø load currents:
Iab = 9A at 53deg
Ica = 17A at 164deg
Ibc = 28A at -83deg
were correct. The magnitudes were consistent with the stated kW and pf (with rounding). The angles were consistent with a starting Vab angle of 90°.

RE: Unbalanced Delta Transformer Loading

jhrist,
You're right. I calculated
'modIAB angIAB' [9.0361] [83.1301]
'modIBC angIBC' [28.1124] [-53.1301]
'modICA angICA' [17.2117] [-165.5730]

The modules are equal.
If you add 30 degrees in each angle that you calculated,
then the angles are equal.
Except ang IAC. - I do not know why they are different!

RE: Unbalanced Delta Transformer Loading

Quote (odlanor)

%for AB,BC,CA phase order VBC reference
a=cos(2*pi/3)+j*sin(2*pi/3);
VBC= 0.415;
VCA= a*VBC;
VAB= a^2*VBC;
Shouldn't VCA = a^2*VBC (-120°)and VAB = A*VBC (+120°)?

RE: Unbalanced Delta Transformer Loading

I do not know how to justify.
Anyone knows?

RE: Unbalanced Delta Transformer Loading

It is simple:
You considered VBC as reference then you get the same modules as jghrist but the angle is different. You have to take VAB=90 [PI()/2] ; VBC=a*VAB and VCA=a^2*VAB and then you'll get the jghrist's results.

RE: Unbalanced Delta Transformer Loading

Hi jghrist,

That is a very interesting post. My results have different phase angles than you guys here. So, should complex apparent power equals to voltage vector multiplied by CONJUGATED current vector?

Regards

RE: Unbalanced Delta Transformer Loading

Yes, S = VI*

RE: Unbalanced Delta Transformer Loading

Zanorter4,
I thought that the modules should be equal and the angles between the three phasors
of reference system should be the same as another reference!

RE: Unbalanced Delta Transformer Loading

You are right, odlanor. The angle between the currents will be the same no matter the reference. But the all individual angle-with respect to the reference-will be different[logical, does not it?].In our case IAB-IBC=136.26 ; IBC-ICA=112.44 ; ICA-IAB=111.3 . SUM[Total]= 360.


RE: Unbalanced Delta Transformer Loading

jghrist
%for AB,BC,CA phase order and load , operator is 1 + a + a^2
see 2.9 connected loads page 34 - Power system analysis-Hadi Sadat

7anoter4
below is the results for 3 reference(VAB,VBC,VCA) and confirm The angle between the currents will be the same no matter the reference.(see Check)
Unbalanced Delta Transformer Loading
thread238-352772: Unbalanced Delta Transformer Loading
odlanor
current module- Ampere
IAB IBC ICA
VAB ref. 9.0361 28.1124 17.1127
VBC ref. 9.0361 28.1124 17.1127
VCA ref. 9.0361 28.1124 17.1127


current angle-Degree check
1+a+a^2 IAB IBC ICA IAB-IBC IBC-ICA ICA-IAB
VAB ref. -36.86 -173.13 74.42 136.27 112.45 111.28
VBC ref. 83.13 -53.13 -165.57 136.26 112.44 111.3
VCA ref. -156.86 66.86 -45.57 136.28 112.43 111.29

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources