Anchor Rod to Vertical Dowel Spacing

Anchor Rod to Vertical Dowel Spacing

Anchor Rod to Vertical Dowel Spacing

(OP)
Is there a code required minimum spacing between an anchor rod and a vertical dowel?

RE: Anchor Rod to Vertical Dowel Spacing

ACI 318, Section 7.6 give spacing requirements between adjacent bars. Is the rod a hooked rod or headed anchor? What is the embedment? What are the forces in the anchor rod? Section 7.6 has minimum spacing requirements between adjacent bars in order to insure that concrete will flow around the full perimeter of the bars, however lap spliced bars are permitted to be in contact with one another.

RE: Anchor Rod to Vertical Dowel Spacing

(OP)
Thanks for the quick reply. Typically they would be headed anchors. Embedment and forces would vary. My thought was as long as I was clearing the head of the anchor I would be ok. Typically I try to keep at least 1" but like you said lap spliced bars are allowed to be in contact so I was curious how others are treating this condition.

RE: Anchor Rod to Vertical Dowel Spacing

I would say it is engineering judgement as to whether the dowel and the headed stud are carrying similar loading.. As in are they both for shear? Or is one a shear element and the other is a tensile element.. If that is the case I would say they could be right next to each other.

If they are to be used additive for shear or tension, I would follow the above recommendation and treat it as a separate rebar and follow those spacing requirements so as to not have a local overstress in your concrete or masonry.

The rebar may have adequate length away from the headed stud / anchor rod so as to not need any development in the region where they touch. In that case, it would be ok.


RE: Anchor Rod to Vertical Dowel Spacing

It depends how you are designing the connection. If you can get the anchors to work out with the App. D calculations for breakout, then there is no minimum or maximum for spacing between anchor rods and pier reinforcing (though, I would still keep the anchors inside the cage). If you need to count on the vertical pier reinforcing to get out of the breakout calculations, then App. D gives a maximum distance between anchor rods and vertical reinforcing, but does not give a minimum.

Don't confuse this with lapping, it's not lapping. You are developing the pier reinforcement above the failure plane of the breakout cone.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources