Air Velocity in Parking Exhaust Duct
Air Velocity in Parking Exhaust Duct
(OP)
Hi
What is the maximum acceptable design velocity for air inside the ducts in a small parking about 6 ft below ground level?
I'm talking with respect to acceptable noise levels/acceptable pressure drop.
The main duct riser will then rise up to the roof of the building through a shaft between apartments.
The shaft is surrounded by kitchens and toilets.
The walls of the shaft are made of 200mm hollow concrete blocks. No sound attenuating materials are to going to be added to the walls.
Do I need to reduce the velocity from that used in the parking lot to reduce the noise further since now the shaft is passing in close proximity with the habitable parts of the building? Or will the walls provide enough sound attenuation?
Best Regards
What is the maximum acceptable design velocity for air inside the ducts in a small parking about 6 ft below ground level?
I'm talking with respect to acceptable noise levels/acceptable pressure drop.
The main duct riser will then rise up to the roof of the building through a shaft between apartments.
The shaft is surrounded by kitchens and toilets.
The walls of the shaft are made of 200mm hollow concrete blocks. No sound attenuating materials are to going to be added to the walls.
Do I need to reduce the velocity from that used in the parking lot to reduce the noise further since now the shaft is passing in close proximity with the habitable parts of the building? Or will the walls provide enough sound attenuation?
Best Regards





RE: Air Velocity in Parking Exhaust Duct
the noise, however, does not come from air flow only, it also comes from fan motor.
there are some ari excel calculation sheets you can find by googling.
RE: Air Velocity in Parking Exhaust Duct
Thank you for the response. You mention exactly what I am looking for.
How much is "too high" a velocity for the parking lot?
And how much is "too high" a velocity for the shaft?
Do the Excel sheets you mentioned calculate noise levels generated in ducts? That's my main concern here.
Best Regards
RE: Air Velocity in Parking Exhaust Duct
RE: Air Velocity in Parking Exhaust Duct
as willard said... there is no silver bullet for that. you cannot just take velocity recommendation and relieve yourself responsibility to do proper engineering work.
for very simple residential calcs, i use 5 m/s as maximum velocity, but only as a rough guide.
it depends much on available space, needed air flow, fan noise... how to decide on it. in general, you should find sleeping room closest to your vertical shaft, than calculate/estimate noise that reaches such room.
RE: Air Velocity in Parking Exhaust Duct
RE: Air Velocity in Parking Exhaust Duct
Thank you for your response. I understand, I thought it was a situation where a rough estimation would work. I'm guessing I'd have to go a bit into sound engineering for this? If you could kindly suggest some relevant Engineering manuals on the topic, I'll be grateful.
Drazen,
Thank you for your response. This project is a small building so I guess a simple rule of thumb would do, but you are right, I should learn more on the topic since I might be faced with more complex problems in the future. Are there any good references that you know?
I'm just guessing but I assume the procedure would be to estimate the noise levels generated by the air flowing inside the ducts, then calculating the attenuation provided by the sheet metal ducts, then that of the block wall, to arrive at the noise level inside the rooms adjacent to the shaft?
317069
Thank you for your response.
RE: Air Velocity in Parking Exhaust Duct
But with duct and a block wall (in the vertical) it sounds similar to a mechancial room, which I design for 1200 fpm and up to 1500 fpm (if not abbutting sound sensitive areas).
800 fpm would definately solve any sound issues you may have (especially where the rooms surrounding the shaft is not bedrooms). Start at 800 fpm, and see if you can have the duct that big. If the architect wants it any smaller, let them know a sound consultant should review if faster velocities can be used (they are notoriusly conservative and may not allow faster velocities). Let them take resposibility, do NOT take acoustic responsibility if velocities are greater than 800 fpm.
knowledge is power
RE: Air Velocity in Parking Exhaust Duct
knowledge is power
RE: Air Velocity in Parking Exhaust Duct
I'm sure there are others.
RE: Air Velocity in Parking Exhaust Duct
you say it is a 6 feet below the ground parking area.
do you mean the parking height is 6 feet only, I doubt, there should be a part of parking wall above the ground and in this case why don't you exhaust it directly to the outside without a duct, does it work this way?
RE: Air Velocity in Parking Exhaust Duct
Thank you for your response, and for the advice. I did it for 850 fpm. The architect did not have any objection since space is not an issue in the area the duct comes up since its located towards the back of the building. As for your advice to request for revision by a sound consultant; that is a luxury I can only dream of. They don't are not operating with that kind of budget on this project. It's a small building an economical solution.I guess some extra sheet metal would do the job here.
willard3,
Thank you for your response. I will look into those, but first I better do some reading on HVAC Acoustics.
317069,
Thank you for your response. You are right, about 4 ft of the basement wall extends above the road level on the front facade only, which I cannot exhaust to. On the 3 other sides the underground basement extends all the way to the property boundary line. So exhausting through the part of the wall above the ground on any of those 3 sides would mean exhausting to the neighboring property.
RE: Air Velocity in Parking Exhaust Duct
knowledge is power
RE: Air Velocity in Parking Exhaust Duct
Your client should review his budget.
RE: Air Velocity in Parking Exhaust Duct
Thank you.
willard3,
You are right, but I don't make these decisions, or liaise directly with clients that much. I'm still at the bottom of the food chain :D
RE: Air Velocity in Parking Exhaust Duct
RE: Air Velocity in Parking Exhaust Duct
The question is why you should bear the risk if some one does not want to spend the money.If I were you and had a similar situation on my hands,I would put in sufficeint caveat clauses in the design brief so that the client can not go after me if anything goes wrong.For eg the car park fans will operate only during certain hours during the day(no operation in the night to disturb anyone's sleep.Provide a generous estimated noise level which would be best verfied by an acoustic consultant etc.In addition to the above specify ultra quiet fans operating at low speeds.
RE: Air Velocity in Parking Exhaust Duct
SMACNA rates ductwork by pressure class, normally, you're in the 2" SP category for such ductwork, with a 2"SP you are essentially in the "low pressure" category as it used to be called - i.e up to 2000 FPM.
RE: Air Velocity in Parking Exhaust Duct
knowledge is power
RE: Air Velocity in Parking Exhaust Duct
RE: Air Velocity in Parking Exhaust Duct
Do you mean if we use 3500fpm in a 10" duct with 2" static pressure we will have a sound issue, but is we add more dampers to same duct and make it with let say 10" static pressure we will not have a sound issue,
Or in other word, if we consider same air velocity in both return and supply duct of a system, would be a difference in sound velocity between the supply side and the return side of the same system in this case they have the same air velocity , but different pressure
RE: Air Velocity in Parking Exhaust Duct
willard3,
Thank you for your response. You are right again. But sometimes nobody is willing to listen. I would elaborate more, but since I am posting from work that might not be the best of ideas, and I don't want to end up venting non-technical related matters on here.
SAK9,
Thank you for your response. That is very valuable information. I will keep that in mind.
cry22,
Thank you for your response. I am quite doubtful about 2000 fpm being quiet enough for a residence. In a factory setting maybe, but I haven't come across velocities that high in residential before.
cdxx139,
Thank you for your response.
sprinkler1000,
I think that up to 1200 might be O.K, but I would not want bear the risk since it's outside my specialty.
317069,
Thank you for the response.
RE: Air Velocity in Parking Exhaust Duct
RE: Air Velocity in Parking Exhaust Duct
Thanks for your response. I've already finished the project and submitted it, but thanks for the tips regardless :)
Best Regards
RE: Air Velocity in Parking Exhaust Duct
Thanks for the response
RE: Air Velocity in Parking Exhaust Duct
Actually I had two very similar projects. I did one as induced draft, and the other was forced draft. In one of them there was no place for a shaft for the duct to go up to the roof so I had to place the fan in the parking in a noise-isolating cabinet, and let the air out at an empty space at backside of the building. I don't really have a lot of information on this issue actually. I would be grateful if you could explain some of the implications of each type of system. Thanks.