Strainers on CW inlet on seal flush coolers
Strainers on CW inlet on seal flush coolers
(OP)
Hi
We have a poor quality of cooling with debris and other
Things in the cooling water. This causes plugging of the
Conical strainers on the inlet to the seal flush coolers.
Are there any suggestions to try to avoid this in terms of
Strainer designs or other options.
Thanks
We have a poor quality of cooling with debris and other
Things in the cooling water. This causes plugging of the
Conical strainers on the inlet to the seal flush coolers.
Are there any suggestions to try to avoid this in terms of
Strainer designs or other options.
Thanks





RE: Strainers on CW inlet on seal flush coolers
My motto: Learn something new every day
Also: There's usually a good reason why everyone does it that way
RE: Strainers on CW inlet on seal flush coolers
Are you taking suction from a Cooling Tower Basin?
If so then I suggest you install some Trash Screens between the Basin and the Suction Pits.
prognosis: Lead or Lag
RE: Strainers on CW inlet on seal flush coolers
However, there are many ways of pre-cleaning the water, say using a buffer tank for settling the debris or a cyclone separator as mentioned earlier. You might also want to use a duplex strainer with a switching valve for cleaning the clogged side while operating the clean side.
Cheers,
gr2vessels
RE: Strainers on CW inlet on seal flush coolers