VFD with Dahlander winding motors

VFD with Dahlander winding motors

VFD with Dahlander winding motors

(OP)
Dear all,
I have been reading threads 237-345587 and 237-268932, still I feel I need some advice.
We have small (4.4/3.3 kW) 2-4 poles motors that originally were meant to run at two fixed speeds.
The winding is Dahlander YY/delta.

Now we have to add a VFD to get ramps and unlimited number of speeds (of course taking care of
heating at low speeds and loss of torque over 50 Hz). The load is a rollerway carrying material,
so more or less constant torque application.

I wonder if I can simply connect the VFD wiring the motor at low speed without any rewiring etc.
After all, the VFD will see a winding - it does not know that it can be arranged in a different way ...

Thank you

RE: VFD with Dahlander winding motors

Yes, of course you can. As long as the VFD outputs the correct V/f ratio.

That's the quick and easy answer. And it will probably work quite well. At least for some time.

If the motor is an older one, and Dahlander motors usually are, then the windings will have a problem with the steep PWM edges and the ringing. After some time, most "Non-VFD" motors break down because of ozone produced by partial discharge and you will have to rewind or change the motor.

You can avoid the insulation problems by adding motor reactors, but they may cause other problems. The most common is that the reactors can get quite hot if the motor cables are long (ringing between reactor leakage inductance and cable capacitance). The ringing can be reduced by adding parallel resistors to the reactors

But I think that it will be better in the long run to buy a standard VFD "hardened" motor. You will get a working installation and don't have to worry about problems popping up when you least want it. Keep the Dahlander motor as a spare.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: VFD with Dahlander winding motors

(OP)
Thank you, it is always very helpful exchanging ideas with people in the know.

RE: VFD with Dahlander winding motors

Your motor is a constant torque 2-speed motor. I would not expect you can run over 50Hz under load so using the high speed connection may be more suitable for your application.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources