Multilin Generator Protection

Multilin Generator Protection

Multilin Generator Protection

(OP)
Setting up 2 MVA, 4160 Genset Protection Relay. I notice input settings for a transformer (Not CPT) and the manual makes reference to transformer differential. What transformer information should be entered... utility by chance?

RE: Multilin Generator Protection

Which relay? GE make at least three or four generator relays.

RE: Multilin Generator Protection

(OP)
G-30 - Looks like they expect a step up/down after generation. I think I should just ignore this setting.

RE: Multilin Generator Protection

I would suggest carefully reading section 5 of the manual. It deals with GE's concept of sources. If not connected via a Transformer, perhaps consider entering the XFMR as a 1:1 voltage ratio with all windings connected wye (star)-wye (star). If unsure, you really have to test with relay test set to get a feel.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources