hello all,

i am running feeders to (2) 3 phase , 480V, 75HP pumps. FLA for each pump is 96A and they are located at a distance of 176 feet from the panel.
according to code:

96A * 1.25 = 120 A, then adjusting for voltage drop gives me #1/0 wires

now do i need to add derating factor if i am running feeders to both pumps in one conduit OR it is either or (voltage drop or derating but not both)? meaning one will cancel the requirement for the other?
if i have to do adjustment for derating then i ll end up with #3/0 which is too large??

thank you,

RE: Voltage drop and derating combined ?

Apply all deratings/adjustments independently and then use the largest conductor that any one requirement necessitates. Note that if you increase the size of the phase conductors for voltage drop you also have to increase the size of the grounding conductor proportionally.

So if your conductor sized for voltage drop without considering multiple conductors is large enough when you consider multiple conductors but not voltage drop then you're good to go.

RE: Voltage drop and derating combined ?

(OP)
Thank you for the response, this makes sense now since counting for both makes the conductors too large.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources