NERC PRC-23 Line Loadability

NERC PRC-23 Line Loadability

NERC PRC-23 Line Loadability

(OP)
I have been looking at the standarded PRC-23, which is in place to prevent loading and operator actions from tripping a relay. I have a long 345 kV line that has enough line impedance to limit the fault current far below out neighbor we are interconnect to short term thermal rating of the line. I am supposed to evaluate the loading of the line with 0.85 percent voltage and 30 degree power factor angle.

The part I don't get is that in the worksheets they draw a line from origin at 30 degrees representing the load and from that you get Zrelay30, which is point the line intsects the zone protection. Why isn't the 30 degree load line drawn so that it intersects the impedance point that represents the end of the line?

http://www.nerc.com/docs/standards/sar/Relay_Loada...

My artistic rendering of what I am talking about.

http://ge.tt/58RbA1s

RE: NERC PRC-23 Line Loadability

It perhaps because of zone3, the over reach of the normal configuration of the line, which is a typical 200%.

RE: NERC PRC-23 Line Loadability

(OP)
Why does the nerc load go through the origin instead of the point that represents the end of the line?

RE: NERC PRC-23 Line Loadability

Because the relay is at the origin, not at the end of the line.

RE: NERC PRC-23 Line Loadability

(OP)
At maximum loading, won't the impedance point be near the line impedance?

RE: NERC PRC-23 Line Loadability

Load impedance is much less than fault impedance

RE: NERC PRC-23 Line Loadability

Make a comment on my previous reply - "Load impedance is much less than fault impedance "
Normally it is true but in some case where it is not true, then the load encroachment will be use to overcome the issue

RE: NERC PRC-23 Line Loadability

Sorry, the fault impedance is less than the load impedance, I meant. What I am doing today sad

RE: NERC PRC-23 Line Loadability

As seen from the relay, a fault at the end of the line has the line impedance to the fault, lots of X and a bit of R. Load, on the other hand is mostly R with a bit of X thrown in for grins and giggles.

Figure out your emergency rating, add 50%, give it a 30 degree angle, assume 85% nominal voltage and plot what the relay sees. Then draw a line from the back to th origin, probably comes out pretty close to 30 degrees.

RE: NERC PRC-23 Line Loadability

david is correct, but a little over simplestic. You also need to read attachment A because it has a few hooks.

Most of us use use the first requirment to meet the standard for lines, although there are twelve other ways to meet the standard.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources