13.8_kV line over a pressure reducing station (Natural gas).

13.8_kV line over a pressure reducing station (Natural gas).

13.8_kV line over a pressure reducing station (Natural gas).

(OP)
A customer called us because they have a pressure reducing station (Natural gas). It is located in the open and on it goes a 13.8_kV distribution line. The client is concerned about the possibility of an accident if one of the lines fall on the gas station, so the customer wants to place a cooper wire mesh below the line with two down conductors for grounding.

I have no references on this type of protection system so I was wondering if anyone could know what standards could be applied to the design of a system like the required (API, IEEE, IEC...). Thanks in advance.

RE: 13.8_kV line over a pressure reducing station (Natural gas).

I don't know of any standard other than the NESC Section 234 that may be applicable. I wouldn't try to engineer a "just in case" solution because if it fails the the blood is on everybody's hands, including yours for agreeing to the solution, if there is an accident. I would also be concerned with the Gas Co. doing maintenance work at this location and making contact with 13.8kV with a crane or other equipment if the line truly runs directly over their equipment.

The best fix would be to relocate the overhead line for a couple of sections, either to a new location away from the Gas Co. equipment or even underground. I've had to deal with something similar in the past with another 3rd party (not Gas Co).

A $15K-$20K line relocation has a better payback than a $5M-$10M lawsuit.

RE: 13.8_kV line over a pressure reducing station (Natural gas).

(OP)
I totally agree with you and really appreciate your comments, We will propose relocating the line.

Thanks!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources