Spacing between fire hydrants

Spacing between fire hydrants

Spacing between fire hydrants

(OP)
Dear All,

Is there anywhere in NFPA codes mention of spacing between two respective fire hydrants for different occupancies. I have not been able to find one, so far. If someone can help please.

Cheers Mates.

RE: Spacing between fire hydrants

In the For What Is Worth department there may be more but from the International Fire Code, 2006 Edition, Section 508.5.1

Quote:

Fire Hydrant Systems: Where a portion of the facility or building hereafter constructed or moved into or within the jurisdiction is more than 400 feet (122m) from a fire hydrant on a fire apparatus access road, as measured by an approved route around the exterior of the facility or building, on-site fire hydrants and mains shall be provided where required by the fire code official. Exception: For buildings equipped throughout with an approved automatic sprinkler system, the distance shall be 600 ft.

From NFPA 24 " Standard for the Installation of Private Fire Service Mains and Their Appurtenances" - 2002 Edition Section 7.2 having to do with number and location of hydrants.

Quote:

7.2.1* Hydrants shall be provided and spaced in accordance with the requirements of the authority having jurisdiction.

RE: Spacing between fire hydrants

(OP)
Many Thanks for the reply, mate. cheers

RE: Spacing between fire hydrants

Yes, I think NFPA 24 v2010 "mentions", and defers, "spacing" of hydrants basically to the authority having jurisdiction. [That being said, I believe designers are probably increasingly using GIS etc. in fire and other flow analyses and models, and to help in determining "spacing" for hydrants and valves etc. to satisfaction of authority(ie)'s requirements.]

RE: Spacing between fire hydrants

I agree with RCONNER about the NFPA and the local jurisdictions, however, the insurance industry also banks on the number of hose streams which one fire hydrant may be able to provide.

RE: Spacing between fire hydrants

Most trucks only carry 500' of supply line, the length that the local FD carries is/will come into play.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources