can a UPS rectifier be used as a power supply?
Hey folks,
sorry to bother people if this is the wrong forum. I'm looking for help regarding these devices:
Link
The issue is I have an industrial laser with the requirements for 48VDC at 50 Amps power supply. I've done a fair amount of electronics work but unfortunately I dont really get the difference between the rectifier and a standard linear power supply. Is it that the rectifier adjusts its voltage for charging UPS batteries? The rectifier documentation talks about a sense lead, is this to control the voltage level?
The docs also state: "..this system will operate as a BATTERY-LESS SYSTEM and do es not require batteries to function." but I'm just getting an independent reality check.
Other question. For most rectifiers, they usually say they are -48VDC, as in "minus 48 volts". Does that mean what I think it means? Could reverse the polarity and treat the negative side as rectifier as the "positive" side of power supply to get +48?
thanks,
owen
Link
thanks,
owen
RE: can a UPS rectifier be used as a power supply?
Modifying this could cause some problems if the positive terminal is grounded internally or internal protection functions monitor this terminal and operate to de-energize this unit should they measure some threshold above or below ground.
It is also possible that some internal components may have voltage ratings selected with its intended operation (positive terminal at ground) and changing this will unduly stress these components over time.
Is it possible to connect your load such that its positive terminal operates at ground? Of course, the load issues would be much the same as those for the supply (internal connections, protection circuits, voltage stress).
To clarify: the rectifiers have two sets of output terminals from the common output. The terminals intended for battery connection will have a current sensor on that branch. The main output terminals may not have a current sensor, or at least if there is it will be for overload protection. If you don't connect a battery then it probably won't cause you any concern.
"Will work for (the memory of) salami"
There are models available that can be used as a straight out power supply.. Some of the very old stuff required additional capacitor banks since the batteries (not there in this application) provided additional filtering..
Think of "chargers" as power supplies having additional control functions available.. Most in this category of power systems available today are switching power supply based and microprocessor controlled with lots of options in the software to configure it to operate according to your needs.. lots of things you probably won't need (temperature profile voltage control, charging profiles, etc) just turn them off in the config... Another common use of these power supplies without batteries to provide the DC for metal plating operations.
Any precision power supply (as these are) employ remote sensing (and if for some reason that wasn't wired in, would operate off of a default profile, or flag it as a critical fault and not start up). Certainly best to install it as designed.
A manufacturing tech rep could help you select a unit to meet your needs..
Alpha Technologies out of Vancouver, BC is one of the most forward thinking, advanced technology companies I've dealt with.. http://www.alpha.com/ This stuff is premium quality as it is built to demanding standards for reliability and performance. There are many others out there...
But check this key point in any prospective unit you consider..