Wind loads for Exposed portal frame per 1170.2-2011 Appendix E

Wind loads for Exposed portal frame per 1170.2-2011 Appendix E

(OP)
Hi All,

I am currently working on a project to be built in Darwin. It is a skillion roof structure with no walls, 42m wide x 105m length with 6m clear height at the low side. It has 16 portal frames spaced at 7m and a 800WB member size. Following the guidelines listed in Appendix E of 1170.2 I am getting considerably high loads. Approx 4.6kN/m wind load along the portal frame profile. The total loads are way more than compared to a fully enclosed condition. Has anyone here had a similar job? Are there any ways to reduce the loads from exposed steel members that is acceptable?

pu: 2.78kPa
Ki: 1.0
Kar: 1.0
Ksh: 1.0
Cfx: 2.05
Cfig: 32.8 (considering 16 portal frames)

Thanks in advance for the responses!

hrbrt372


RE: Wind loads for Exposed portal frame per 1170.2-2011 Appendix E

The 4.6kN/m seems reasonable for a design. For an open structure I use a minimum design of 0.35kPa for serviceability and 0.75kPa for ultimate designing assumming that the structure is hypothetically enclosed. The Cfig of 32 doesn't sound right.

RE: Wind loads for Exposed portal frame per 1170.2-2011 Appendix E

(OP)
Thanks for the reply asixth.

I have 16off portal frames and each portal frame has cfig1 = 2.05. On equation E2(5) in AS 1170.2 Cfig is equal to the summation of Cfig1 of each portal frame.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close