Bonding of pipe sections and bond/ground testing Frequency
Two Questions in one post:
1) Is there any regulation/code/standard on the need for star washers (to make a 'better' bond) between two pipe flanges....in pipe carrying liquid hydrocarbons (monomers, in particular)? I always thought that the flange bolts themselves were good enough to bond the pipe together (even if painted) with the added benefit of the pipe usually bonded/grounded to the structure anyway.
2) Is there a required testing frequency to verify the bond is still good? How about a testing frequency for earth grounds in general?
______________________________________________________________________________
This is normally the space where people post something insightful.
RE: Bonding of pipe sections and bond/ground testing Frequency
According to NEC art.250.8 "Connection of Grounding and Bonding" equipment pressure connectors has to be listed as grounding and bonding equipment. See [for instance]:
http://www.erico.com/public/library/fep/LT0359.pdf