MagneticBalance Test

MagneticBalance Test

MagneticBalance Test

(OP)
Hello everyone,
We conducted a magnetic balance test on a 30MVA, 132/33KV transformer on all the taps at both primary and secondary. The results showed that the sum of the two voltages are different from the applied voltage by about 6V to 10V. Is this acceptable? What could be wrong please.

RE: MagneticBalance Test

Is neutrsl ground removed ?

RE: MagneticBalance Test

(OP)
Yes it is removed.

RE: MagneticBalance Test

I would not bother too much if measured voltages on other two limb do not add upto applied voltage as long as excitation current for each limb is identical

RE: MagneticBalance Test

We allow +/-5 % on the outside limbs but do expect equality when testing the middle limb.

RE: MagneticBalance Test

(OP)
Thanx a lot

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources